Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84865members
354358posts

PCNS/vCenter Best Practices

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
mwhalen_apc
Lieutenant
Lieutenant
0 Likes
4
492

PCNS/vCenter Best Practices

This was originally posted on APC forums on 5/8/2015


Hello,

I'm just in the beginning phases of figuring out a good way to use PCNS in this environment. Here are the specs:

A SmartUPS 5000 RM XL with NMC

Two ESX hosts managed by a vCenter VM on one of the hosts. This is an HA cluster with vMotion.

In the past, I've deployed the PCNS VMWare OVF (appliance) on ESX and used it to manage a host directly. (I did try once managing a single host through vCenter in which both vCenter and PCNS were VMs on that same host, but I never could get the timing right. Either PCNS would lose connectivity because it shutdown too soon or PCNS couldn't finish its script because the vCenter VM powered down before PCNS.)

I have two questions:

  1. Should we look to put PCNS on a physical workstation outside the cluster? We can do it, but we'll need to purchase something.
  2. Is it really not possible to run PCNS in a VM and use it to manage shutdown of a VM vCenter when both are on the same physical host?

Accepted Solutions
mwhalen_apc
Lieutenant
Lieutenant
0 Likes
0
492

Re: PCNS/vCenter Best Practices

This was originally posted on APC forums on 5/12/2015


Wow. Wonderful. I'll check that out. Thanks again.

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
492

Re: PCNS/vCenter Best Practices

This reply was originally posted by Bill on APC forums on 5/9/2015


Mike,

You should review Application Note 180 and the user's guide. They provide information concerning set-up and configuration possibilities.

On 5/8/2015 3:22 PM, Mike said:

  • Should we look to put PCNS on a physical workstation outside the cluster? We can do it, but we'll need to purchase something.
  • Is it really not possible to run PCNS in a VM and use it to manage shutdown of a VM vCenter when both are on the same physical host?

  1. You do not need to install PowerChute on a standalone system but you can. That possible configuration is discussed on page 3 of the application note.
  2. You can run PowerChute appliance and vCenter on the same host. That configuration is discussed on page 4 of the application note.

 

mwhalen_apc
Lieutenant
Lieutenant
0 Likes
0
492

Re: PCNS/vCenter Best Practices

This was originally posted on APC forums on 5/12/2015


Hi Bill,

Thanks for the information about Application Note 180. I have read it since you wrote. 🙂

On 5/9/2015 9:00 AM, Bill said:

You can run PowerChute appliance and vCenter on the same host. That configuration is discussed on page 4 of the application note.

Ok, I'll give this a go again. However, I don't quite understand something.

The Note seems to indicate that after vCenter has shut down there is a timeout period and, upon expiration, PowerChute will proceed with shutting down anything else. In other words:

  1. UPS goes on battery ... other things are shut down.
  2. vCenter is shut down.
  3. PowerChute loses connection with vCenter (because it's down) but waits for a time and then continues anyway.

Is this accurate? If so, what is that timeout period?

Thanks, Bill!

Cheers,

m

BillP
Administrator Administrator
Administrator
0 Likes
0
492

Re: PCNS/vCenter Best Practices

This reply was originally posted by Bill on APC forums on 5/12/2015


Hi

On 5/12/2015 11:43 AM, Mike said:
  1. UPS goes on battery ... other things are shut down.
  2. vCenter is shut down.
  3. PowerChute loses connection with vCenter (because it's down) but waits for a time and then continues anyway.

Is this accurate? If so, what is that timeout period?

Yes. That is accurate. The time out period is configurable. It is set under the heading of Virtualization Settings - vCenter Server VM Shutdown Duration. The default delay is set for 240 seconds / 4 minutes.

Attachments
mwhalen_apc
Lieutenant
Lieutenant
0 Likes
0
493

Re: PCNS/vCenter Best Practices

This was originally posted on APC forums on 5/12/2015


Wow. Wonderful. I'll check that out. Thanks again.