Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and we have a new, shorter address that's easier to remember. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82632members
350282posts

PCNS Delay clarification in Configure Events

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
knowlesy_apc
Ensign
Ensign
0 Likes
2
93

PCNS Delay clarification in Configure Events

This was originally posted on APC forums on 4/11/2016


Hi,

Im intrigued about the delay for the likes of  "UPS on Battery", "Contact Zone 1 Alarm" and "Communication lost while on Battery" 

So for the likes of "UPS on Battery"

  • does is this a delay before the UPS or the VMS shutdown or is this replaced by vm prioritization ?
  • does this delay give you x amount of time to do anything so for instance you can put a delay in for changing over power supply to the ups
    • Or in a similar situation the power has tripped for X amount of time wait a delay of XXX before things start to happen ? 

Cheers 


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
93

Re: PCNS Delay clarification in Configure Events

This reply was originally posted by Bill on APC forums on 4/12/2016


Hi,

The delays would be prior to the beginning of the shut down. Example: configure OS to power down 120 seconds after UPS has transferred to battery. The NMC will inform PCNS that the UPS is on battery and PCNS will wait 120 seconds before starting the shut down process. If the NMC report it has transferred back to AC within the 120 seconds PCNS will not start the shut down process. 

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: PCNS Delay clarification in Configure Events

This reply was originally posted by Bill on APC forums on 4/12/2016


Hi,

The delays would be prior to the beginning of the shut down. Example: configure OS to power down 120 seconds after UPS has transferred to battery. The NMC will inform PCNS that the UPS is on battery and PCNS will wait 120 seconds before starting the shut down process. If the NMC report it has transferred back to AC within the 120 seconds PCNS will not start the shut down process. 

knowlesy_apc
Ensign
Ensign
0 Likes
0
92

Re: PCNS Delay clarification in Configure Events

This was originally posted on APC forums on 4/12/2016


Thanks for the clarification Bill as always most insightful and clear!