Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84497members
353716posts

PCNS Configuration

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
362

PCNS Configuration

This question was originally posted by Joe on APC forums on 6/1/2017


Even after reading a number of posts and articles on this subject I still find it confusing.

If I configure the NMC to initiate a shutdown event with 15 minutes of run time remaining do I still need to configure shutdown events in PCNS or can I leave them at default (greyed out)?

Thanks >> Joe

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
361

Re: PCNS Configuration

This reply was originally posted by Joe on APC forums on 6/5/2017


Perfect.

Thanks >> Joe

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
362

Re: PCNS Configuration

This reply was originally posted by Bill on APC forums on 6/2/2017


Hi,

When the UPS reaches the low battery threshold the NMC sends a signal the each of the configured PCNS clients and they start the OS shutdown process. You do not need to configure anything else within PCNS. Likewise if the UPS has switched outlet groups and the outlet group reaches the defined shutdown range NMC sends a signal the each of the configured PCNS clients and they start the OS shutdown process.

BillP
Administrator Administrator
Administrator
0 Likes
0
362

Re: PCNS Configuration

This reply was originally posted by Joe on APC forums on 6/2/2017


So is my following layman's understanding correct?

Configure shutdown on the NMC and only the NMC if:

  • you want all the connected PCNS clients to shutdown in the same manner/schedule.
  • you you want the UPS to turn off before completely draining the battery.

Configure shutdown in PCNS if you want the server/machine to respond differently than the NMC setting.

Thanks again.  You are a breath of fresh air.

Best >> Joe

BillP
Administrator Administrator
Administrator
0 Likes
0
362

Re: PCNS Configuration

This reply was originally posted by Bill on APC forums on 6/5/2017


On 6/2/2017 4:43 PM, Joe said:

Configure shutdown on the NMC and only the NMC if:

  • you want all the connected PCNS clients to shutdown in the same manner/schedule.

Correct.

On 6/2/2017 4:43 PM, Joe said:

you you want the UPS to turn off before completely draining the battery.

This will happen even if you select a configurable PowerChute Shutdown event. You can configure PowerChute to turn the UPS off or the UPS will power it self down once the batteries get low. When the UPS reaches low battery it will wait the low battery duration, then the UPS turn off delay, then a built in 2 minute dealy that is non configurable and finally power down.

On 6/2/2017 4:43 PM, Joe said:

Configure shutdown in PCNS if you want the server/machine to respond differently than the NMC setting.

Correct. 

BillP
Administrator Administrator
Administrator
0 Likes
0
362

Re: PCNS Configuration

This reply was originally posted by Joe on APC forums on 6/5/2017


Perfect.

Thanks >> Joe