PCNS Command file path not accepted

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

iomasm
Cadet
0 Likes
1
253

PCNS Command file path not accepted

Hello,

 

i have a very strange problem. I have tried to run a command file for shutting down the netapp but as you can see in the image the folder i use is not accepted. Everything seems ok but i don't know what is it's problem.

I have installed PowerChute 4.4 and i didn't find anything on bugs.

Any ideas???

image.png

Tags (1)
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
207

Re: PCNS Command file path not accepted

@iomasm 

 

You should verify the file custom_script.sh is an executable. To do so log into the PowerChute VM. Go to the user-files directory and enter the command ls -la If custom_script.sh is not listed as -rwxr-xr-x for permissions enter chmod +x custom_script.sh

 