Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:04 AM . Last Modified: 2024-03-18 12:55 AM
Does somebody know what happens if my ATS (AP7721) exceedes the 10A (Europe, 230V) maximum corrent limit?
Reading specifications, it has no overload protection.
So, after some amount of time in overload, may it brake itself?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:04 AM . Last Modified: 2024-03-18 12:54 AM
It would alert you about an overload from the network management card in the ATS and front LCD display and then it'd rely on upstream protection (like a circuit breaker) at your electrical panel. That should be sized appropriately according to what you see in this document -> http://www.apcmedia.com/salestools/ASTE-6Z6KBC/ASTE-6Z6KBC_R4_EN.pdf which says external protection recommended, 16A.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:04 AM . Last Modified: 2024-03-18 12:54 AM
It would alert you about an overload from the network management card in the ATS and front LCD display and then it'd rely on upstream protection (like a circuit breaker) at your electrical panel. That should be sized appropriately according to what you see in this document -> http://www.apcmedia.com/salestools/ASTE-6Z6KBC/ASTE-6Z6KBC_R4_EN.pdf which says external protection recommended, 16A.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.