Outlet Sequence delay plus Shutdown Procedure delay, or not?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
chrisbbb_apc
Ensign
Ensign
0 Likes
1
121

Outlet Sequence delay plus Shutdown Procedure delay, or not?

This was originally posted on APC forums on 9/25/2016


UPS SMX2200HV & PowerChute Business Edition 9.1.1 Build 604

Initial Settings - Shutdown Settings - Power Fail Config  - set to "begin shutdown procedure after the UPS as been on battery for" 300secs.

Outlet Sequence - "Time for other apps to shut down" 30secs plus "Time for os to shut down" 180secs, "Total time for outlet Group 1 to shutdown" 210secs.

My question: if the inlet mains power to UPS goes off, does Outlet Group 1 shut down 210secs later, or 510secs later?

Thanks

Chris


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
121

Re: Outlet Sequence delay plus Shutdown Procedure delay, or not?

This reply was originally posted by Bill on APC forums on 9/26/2016


Hi,

The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
122

Re: Outlet Sequence delay plus Shutdown Procedure delay, or not?

This reply was originally posted by Bill on APC forums on 9/26/2016


Hi,

The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds.