Outlet Group Shutdown - how to cancel if power is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

baze72
Cadet
0 Likes
1
303

Outlet Group Shutdown - how to cancel if power is restored

I have my Power Group outlets - power off delay set to 480 seconds. I have a question:

 - Is there a way to cancel this shut down if the AC power is restored?

 

Thanks!

 

Tags (1)
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
278

Re: Outlet Group Shutdown - how to cancel if power is restored

@baze72 

 

You can cancel using the network card of via the LCD panel. Using the network card go to Control - Outlet Groups. 

Via the LCD go to control. 

 