Old UPS - trying to see if it works

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Old UPS - trying to see if it works
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:39 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
4
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:39 PM . Last Modified: ‎2024-03-06 10:46 PM

Old UPS - trying to see if it works

I have a Smart UPS 3000xl that was here at my employer when I started last March.  Nothing was connected to it and it wouldn't power up. 

Have a little bit of time now and am trying to determine if it is usable or should be scrapped.  Has an external battery pack.  I know it's a discontinued model, and I'd rather get a new one, but frankly, disposing of it would be quite the pain.  If I can get it to work even for non-production use, it'd be better than trying to get rid of it.

UPS is SU3000RMXL3U

External battery is SUA48RMXLBP3U

First thing I did was check all the batteries - they were all dead.

So I bought 8 batteries on ebay and replaced all the batteries in the internal 48VDC pack, disconnected the external battery pack.  Unit still wouldn't power up.  Verified AC power and checked breaker.  Checked voltage on battery pack and it's around 50VDC.

So I took off the top cover.

When I trace the wiring for the internal battery pack, the blue connector that the internal battery plugs into is attached to some heavy gauge cable.  The black ground runs from the front connector to a similar blue connector (one of a pair) in the rear of the unit.  Red hot takes a similar path, although has some device inline (fuse?).  I checked voltage at the rear blue connector, and it's 50VDC.

The odd thing is this voltage never gets to the internal UPS circuitry.  I don't see how the internal batteries could ever power the unit, much less get charged.  The internal circuitry is connected to another blue connector on the back of the unit, right next to the one that connects to the internal battery pack.  I could plug an external pack into this second connector after replacing its batteries, but that still doesn't explain how the internal battery pack connects to the UPS circuitry.  I checked the two blue connectors in back and they are isolated from each other.

Is there supposed to be some sort of jumper across the two blue connectors in the back?  I don't see how else the internal battery pack would ever power anything.  The user manuals for the UPS and for the external battery pack don't even note the second connector being there or speak of a jumper.

Any ideas?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

I think you're right. It looks like SUA48RMXLBP3U has a connector on the back for daisy chaining additional battery packs, although using it for what's supposed to be the internal battery would be a bit funny.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:39 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:39 PM . Last Modified: ‎2024-03-06 10:46 PM

So, I noticed the blue connector on the internal battery pack matched the blue connector on the back of the UPS where the external battery pack plugs in.

So I pulled the internal battery pack, hauled it around to the back of the unit, and plugged it in.

Fans cycled, and the UPS fired right up after pressing the on button.

So, the good news is the UPS works, and I can take the 8 batteries out of the internal battery pack, use them to replace one bank of the external battery pack, and get 8 more for the second bank of the external pack.

Bad news is I still haven't figured out how to actually connect the internal battery pack to the UPS.  The way it's looking now, the unit shipped with batteries and they were never used - they just slowly discharged over time because the internal pack isn't wired to anything internally when you plug it into it's blue connector on the front.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

The internal and external battery connectors should be connected in parallel. Maybe there's a blown fuse.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

I found a blue plug on ebay that appears to be some sort of jumper that would span the two rear plugs and connect the internal battery pack back into the UPS unit.

(Here's a link, although it expires in about 8 hours: http://www.ebay.com/itm/161358457554?_trksid=p2055119.m1438.l2649&ssPageName=STRK%3AMEBIDX%3AIT)

The diagrams in the user manual for the external battery pack show what appears to be a double plug with four wires (presumably twohots and two grounds) plugging into the two plugs on the back of the UPS unit simultaneously.  It also states that the last battery pack needs to have the plug cover (jumper) on it. 

From this, it sounds to me like the UPS I have jumpers the internal battery externally using this jumper, either at the back of the unit, or at the back of the last external battery.  The second pair of wires are used to jumper the internal battery.  My external battery pack doesn't have provisions for this - it only has a two wire plug and a similar receiving plug for another external battery.  No place for a dual-plug jumper to relocate.

 

Unfortunately, there's no one at the company who was here when this thing was purchased (around 2006).  It sounds to me like there was a design change and the UPS and external battery are a mismatch.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:40 PM . Last Modified: ‎2024-03-06 10:46 PM

I think you're right. It looks like SUA48RMXLBP3U has a connector on the back for daisy chaining additional battery packs, although using it for what's supposed to be the internal battery would be a bit funny.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of