OID and MIB question on APC UPS units.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • OID and MIB question on APC UPS units.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
grubersnmp_apc
Crewman grubersnmp_apc
Crewman

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
7
8463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

OID and MIB question on APC UPS units.

Hello, I am working towards setting up a remote monitoring system for my work place and I had some questions regarding APC OID's and the APC MIB. I started using GetIf today to narrow down some of the OID's that I want to check and I noticed something that I thought was a bug with a different program that is similar to GetIf. When I walk the MIB tree down I see multiples of the same OID description. They often have values in them but the values seem to be unrelated or are valid values for other OID's. Here are some examples.

.1.3.6.1.4.1.318.1.1.1.2.3.1.0 upsBattery.3.1.0 : 1000

.1.3.6.1.4.1.318.1.1.1.2.3.2.0 upsBattery.3.2.0 : 341

.1.3.6.1.4.1.318.1.1.1.2.3.3.0 upsBattery.3.3.0 : 1200

.1.3.6.1.4.1.318.1.1.1.2.3.4.0 upsBattery.3.4.0 : 1365

This seems to occur multiple times throughout the MIB. Can anyone explain the reason for multiple OID's with the same description but different values?

Thanks,

Jeff Rogers

PS this is coming from a 16kVA Symmetra

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • mib
  • oid
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

"upsHighPrecBatteryCapacity" should not be .1.3.6.1.4.1.318.1.1.1.2.2.1


Make sure you have the latest PowerNet MIB (as of time of writing) from here: PowerNet MIB v4.0.7 (Scroll down to the MIB).


Here's what you should see when you walk the MIB in GetIF:

1136_WalkMIB.png

If it still doesn't work, try weeding out GetIF's MIB folder to the powernet407.mib file and a few others that come with GetIF. Some MIBs I've encountered are malformed and will fool GetIF or otherwise conflict.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

Jeff,

What you have posted are 4 distinct MIB objects in the powernet MIB.

What you are seeing might be a display problem in the way that your program works, because .1.3.6.1.4.1.318.1.1.1.2 is representative of upsBattery in the powernet MIB.

So it is showing you the numerical oid string, and then the textual (as much as the program can) oid. Last is the value,

for item 1, which is upsHighPrecBatteryCapacity expressed in tenths of full capacity (so it's showing 100%)

for item2, which is upsHighPrecBatteryTemperature, expressed in tenths of degrees celsius (it's showing 34.1 degrees C)

etc.

But I am not familiar with getif so I don't know what options are available, but I'd suggest look for an option to print only numerical oids (in net-snmp, it's "-O n"

chris

Reply

Link copied. Please paste this link to share this article on your social media post.

grubersnmp_apc
Crewman grubersnmp_apc
Crewman

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

Ok that does make more sense but that leads me into another question. I see where you are matching those OID's to the description. It doesn't look like it matches up for me however. I guess this is also my fault for not sharing this the first time however I didn't notice.

In the results from the SNMP poll I see :

.1.3.6.1.4.1.318.1.1.1.2.3.1.0 upsBattery.3.1.0 : 1000


In the tree view I see the description that you gave "upsHighPrecBatteryCapacity" that OID is :


.1.3.6.1.4.1.318.1.1.1.2.2.1


In the tree view I dont even have a 318.1.1.1.2.3

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
0
8461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

"upsHighPrecBatteryCapacity" should not be .1.3.6.1.4.1.318.1.1.1.2.2.1


Make sure you have the latest PowerNet MIB (as of time of writing) from here: PowerNet MIB v4.0.7 (Scroll down to the MIB).


Here's what you should see when you walk the MIB in GetIF:

1136_WalkMIB.png

If it still doesn't work, try weeding out GetIF's MIB folder to the powernet407.mib file and a few others that come with GetIF. Some MIBs I've encountered are malformed and will fool GetIF or otherwise conflict.

Reply

Link copied. Please paste this link to share this article on your social media post.

grubersnmp_apc
Crewman grubersnmp_apc
Crewman

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:32 AM

This seems to be the case, I was using a older version and the MIB seems to be incorrect. Everything meshes now thank you!

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

mchugo_apc
Crewman mchugo_apc
Crewman

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

Hi all,

I have a similar issue where i am trying to monitor the phase load on aAPC PDU but the amps are in 10 times what they should be in the readings (reading 16amps but it should be 1.6 amps) theOiD is 

1.3.6.1.4.1.318.1.1.12.2.3.1.1.2

I'd appreciate any assistance as i am trying to get the PDU monitored via WhatsUpGold thanks 

Colin

  • Tags:
  • 1.3.6.1.4.1.318.1.1.12.2.3.1.1.2
  • apc
  • load
  • oid
  • pdu
  • phase
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

Hello, the OID you mentioned has this for its description:

Getting this OID will return the phase/bank load measured in tenths of Amps.

So 16 is really 1.6 because of the description. Does What's Up Gold allow you to format the data somehow so that it can convert 16 to 1.6? Else, you'd need to know this is specifying in tenths.

Reply

Link copied. Please paste this link to share this article on your social media post.

mchugo_apc
Crewman mchugo_apc
Crewman

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

0 Likes
0
8460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:46 AM . Last Modified: ‎2024-03-13 12:31 AM

Thank you Angela no as far as i know what's up gold does not allow this so I am trying to find a work around for this problem. I'd appreciate your or anyone elses help on this one. thanks in advance. Colin

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login