NMC2 communication not established

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC2 communication not established
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
richardkeymer_apc
richardkeymer_apc
Cadet

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

0 Likes
5
1471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

NMC2 communication not established

Brand new APC 1500i and NMC2

All looked good on the desk before installation, updated the firmware to 6.5 and could 'browse' to the web interface, all looked good

Now I'm getting  Local Management-To-UPS Communication Lost

01/11/2018 01:20:13 UPS: The local network management interface-to-UPS communication not established.
01/11/2018 01:20:13 UPS: The local network management interface-to-UPS communication not established.
01/11/2018 01:19:48 MDS: Communication Lost With Metering Board[7..12]
01/11/2018 01:19:48 MDS: Communication Lost With Metering Board[1..6]
01/11/2018 01:19:43 Environment: Integrated Input Contact 4 Critical Alarm

Attached event log

I have removed nmc card for 30 mins and reseated. I have re-installed 6.5 firmware

😞

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:38 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:38 PM . Last Modified: ‎2024-03-11 04:41 AM

Hi Richard - OK, you're very welcome!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

Hi Richard,

It sounds like you loaded the incorrect firmware and we can easily correct this.

Can you confirm the exact model of your UPS?

Can you confirm which firmware you applied?

For Smart-UPS types, this is the correct file that should be applied: ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/sumx/650/apc_hw05_aos650_sum... 

Reply

Link copied. Please paste this link to share this article on your social media post.

richardkeymer_apc
richardkeymer_apc
Cadet

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

Model Number
AP9630
Serial Number
ZA1711003370
Hardware Revision
08
Manufacture Date
03/14/2017
MAC Address
00 C0 B7 DF 1A B8
Management Uptime
0 Days 2 Hours 6 Minutes
I used this firmware:
Network Management Card 2 v6.5.0 Firmware Executable for Symmetra PX 48; 96; 100; and 160 kW Systems SFSYPX2V650
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

Hi Richard,

OK, that firmware is for a Symmetra PX. If you have a Smart-UPS that your AP9630 is installed into (which is my best guess as to what "APC1500I" is for the actual UPS model), use and apply that firmware file I provided a link to and re-check that the NMC is working properly afterwards.

Reply

Link copied. Please paste this link to share this article on your social media post.

richardkeymer_apc
richardkeymer_apc
Cadet

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

Hi Angela,

Yep, it is a Smart-UPS I have, all working fine again now with the firmware from your reply.

Thanks for everything 🙂

Richard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:38 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:38 PM . Last Modified: ‎2024-03-11 04:41 AM

Hi Richard - OK, you're very welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of