NMC shut down 1 of 4 servers for no apparent reason

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC shut down 1 of 4 servers for no apparent reason
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
JRVcr
Crewman JRVcr
Crewman

Posted: ‎2023-06-05 01:16 PM

0 Likes
6
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-05 01:16 PM

NMC shut down 1 of 4 servers for no apparent reason

2 x Smart-UPS SRT 2200 with NMC3 and temperature probe set up as redundant UPSs.

 

"High" temp is set to 24 degrees C, "Maximum" to 27 degrees C.

 

NMC Logs show server room got to 24 degrees at 8:24 AM when the door was left open. Temperature never reached 27 degrees; after 8 minutes it dropped back below the 24 degree threshold.

 

Control Policy on both NMCs is "Environment: A critical fault exists for integrated Environmental Monitor input contact ({name} at {location}): Graceful shutdown."

 

Here's what's in the PCNS log from the server that was shut down:

 

Screenshot 2023-06-05 151041.png

 

  1. Why did it send a shutdown when only "High" temperature was reached, not "Maximum", since policy specifies "critical" event?
  2. Why did it send the shutdown to only 1 connected server? All show connectivity to both UPS's. The other servers show the temp out-of-range events but no shutdown events. I'm glad they didn't, here; the one shutdown caused enough chaos! But I DO want the other servers to shut down if it's too hot. (27 degrees, though not 24.)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-06-06 11:13 AM

0 Likes
1
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 11:13 AM

@JRVcr 

  1. Why did it send a shutdown when only "High" temperature was reached, not "Maximum", since policy specifies a "critical" event? PowerChute will trigger the shutdown when the first threshold has been reached. If you do not want the shutdown triggered for the high-temperature violation, deselect that within the NMC or set the high-temperature threshold to 27. 
  2. You should verify you have configured PowerChute on the other server to trigger a shutdown for a temperature threshold violation. 
Reply

Link copied. Please paste this link to share this article on your social media post.

JRVcr
Crewman JRVcr
Crewman

Posted: ‎2023-06-06 11:57 AM . Last Modified: ‎2023-06-06 12:06 PM

In response to BillP
0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 11:57 AM . Last Modified: ‎2023-06-06 12:06 PM

Bill, you're correct that the one server that shut down has "Temperature Probe 1 Out Of Range" enabled for shutdown in PCNS and the others do not. So I need to fix that. 

 

But, back in NMC, when I add a Control Policy, I'm offered the choice of "Warning" or "Critical".

 

Screenshot 2023-06-06 135157.png

I chose "Critical."

Screenshot 2023-06-06 135524.png

I had expected the NMC would only signal shutdown if the "Critical" threshold was passed. Not the "Warning" threshold. That's not correct? If so, what's the point of having Policies configurable for the two thresholds?

 

The goal was to have the warning at 75 F so one of the people who receives the notifications can block the door open and set up a box fan, where shutdown can be averted by keeping the temp below 80 F until air-conditioning is restored.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-06-07 11:57 AM

0 Likes
1
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-07 11:57 AM

@JRVcr 

 

PowerChute does not differentiate. It will react to either as a critical event. The solution is to add a second AP9335 to port two. Configure port two with the high temp threshold that will send a notification.

 

PowerChtue will only react to port one so configure port one with the max temp threshold that will command PowerChute off.

Reply

Link copied. Please paste this link to share this article on your social media post.

JRVcr
Crewman JRVcr
Crewman

Posted: ‎2023-06-07 12:44 PM

In response to BillP
0 Likes
0
968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-07 12:44 PM

@BillP , thanks for your reply!

 

If I leave the NMC configured as it is--to send a shutdown signal at 27 C--and disable Shutdown on the temperature violation Event in PCNS, will the NMC shut the servers down at 27 C? In other words, is the root of my issue that--at least on this one server--over-temperature shutdown is configured in both NMC and PCNS, when, given my objectives (notification at 24 C, shutdown at 27 C), it should only be configured on the NMCs?

 

Or does PCNS ignore the shutdown signal if it hasn't also been enabled in the PCNS Event?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-06-08 12:22 PM

0 Likes
1
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-08 12:22 PM

@JRVcr 

 

Are you using an AP9335 with the AP9810? If so you will need to create two Control Policies. One for the AP9810 and one for AP9335T/TH

 

On the AP9810 jumper 

Zone A Com to Output Com

Zone A NC to Output NC

Control Policies.png

Input Contact.png

Temp Sensor.png

When the Max temp threshold is breached, the IO state changes, and the UPS powers off and signals PowerChute. PowerChute will shutdown because of the critical UPS turn off event.

PowerChute should not be configured to shutdown for a temperature threshold violation and should not be configured to power off the UPS or Outlet Group. 

NMC Event log.png PCNS Event Log.png

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JRVcr
Crewman JRVcr
Crewman

Posted: ‎2023-06-09 06:38 AM

In response to BillP
0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-09 06:38 AM

I won't be at this client again until Monday, so SKUs are hard to come by at the moment. But we are NOT using AP9810s. The thermal sensors connect directly to the NMC3s.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of