Metered Rack PDU near @ 22.7 amps on failover.....is that too high?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Metered Rack PDU near @ 22.7 amps on failover.....is that too high?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:55 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
5
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:55 AM . Last Modified: ‎2024-03-18 01:06 AM

Metered Rack PDU near @ 22.7 amps on failover.....is that too high?

Hey guys,

I am new to this whole power thing but am slowly learning.  We have a rack at a Colo and they are bringing the A Side power down for an entire week.  This leaves each rack running on B side power only.  One of our racks (the SAN and blade server rack) is now at 22.7 amps.  My question is this:  This PDU is on a 32 AMP circuit but the threshold of the PDU itself is 24 amps.  What does or should that mean to me?  Am I too close to tripping a breaker for comfort or am I okay?

The other issue is if we spin up more VM's (20 more to be exact) it will push the amps up closer to 24 amps.

Looking for someone to educate me on the risk of being this close.  The model PDU we are using is: AP8841

1172_pastedImage_0.png

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

AP8841 PDU is a 30A PDU. Per National Electrical Code here in the US, a circuit is not supposed to use more than 80% of its rating meaning this PDU is de-rated to 24A which is 80% of 30A.

So, your overload threshold is at 24A for the entire PDU because of that 80% rating.

Then each PDU bank (or groups of outlets) is 16A (de-rated 80% from a 20A circuit cause they have 20A breakers) on there I believe so between the two banks, you shouldn't go over 24A and each bank or group of outlets you shouldn't go over 16A.

The breakers actually trip at either 30A (at your panel) or 20A for each bank. It should technically have a 30A breaker and not 32A.

Am I making sense? embarassed

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

AP8841 PDU is a 30A PDU. Per National Electrical Code here in the US, a circuit is not supposed to use more than 80% of its rating meaning this PDU is de-rated to 24A which is 80% of 30A.

So, your overload threshold is at 24A for the entire PDU because of that 80% rating.

Then each PDU bank (or groups of outlets) is 16A (de-rated 80% from a 20A circuit cause they have 20A breakers) on there I believe so between the two banks, you shouldn't go over 24A and each bank or group of outlets you shouldn't go over 16A.

The breakers actually trip at either 30A (at your panel) or 20A for each bank. It should technically have a 30A breaker and not 32A.

Am I making sense? embarassed

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

Hey guys,

I am new to this whole power thing but am slowly learning.  We have a rack at a Colo and they are bringing the A Side power down for an entire week.  This leaves each rack running on B side power only.  One of our racks (the SAN and blade server rack) is now at 22.7 amps.  My question is this:  This PDU is on a 32 AMP circuit but the threshold of the PDU itself is 24 amps.  What does or should that mean to me?  Am I too close to tripping a breaker for comfort or am I okay?

The other issue is if we spin up more VM's (20 more to be exact) it will push the amps up closer to 24 amps.

Looking for someone to educate me on the risk of being this close.  The model PDU we are using is: AP8841

1172_pastedImage_0.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

yes.  you are correct on the 30 amp.  My mistake smile  .  I am also managing each bank as you stated above keeping each below 16 Amps.

So if I am understanding you correctly:  Right now I am at 21.6amps total balanced across the two 16 amp banks.  In theory, If I were to run at, let's say .... 25 amps total for a short period (less than 8 hours), (16 amps on one bank and 9 amps on the other) .. how much risk am a I looking at in tripping a breaker? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

You're within 5 amps of tripping your upstream breaker which brings the whole PDU down tongue-out

So I would make sure there is no fluctuation and expect the PDU to constantly be alarming you (so you might want to tone down your notification settings during this period).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:56 AM . Last Modified: ‎2024-03-18 01:06 AM

Glad to hear!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of