Low runtime on UPS Smart-UPS 3000 RM XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Low runtime on UPS Smart-UPS 3000 RM XL
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
5
2746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Low runtime on UPS Smart-UPS 3000 RM XL

We have 2 Smart-UPS 3000 RM XL nobreaks purchased in the year 2011 whose batteries have been replaced but the runtime between them is very different.

Nobreak #1 was changed to battery in November 2016 and nobreak #2 was changed to battery in February 2016. We did the calibration procedure as indicated, but the runtime still remains very different.

Note that in the nobreak that has been changed the battery most recently has the lowest runtime.

Any suggestions on how to proceed.

Nobreak #1

Nobreak #2

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • low
  • runtime
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi Emerson,

Click on the Shutdown option for "UPS on battery" event and check on the box of "Enable Shutdown", now set the delay for the shutdown. It takes in seconds so you need to convert minutes to seconds and add it. Ex: to set the server to shutdown after 5 minutes of power outage I would multiply by 60 and set the delay as 300 seconds.

Regards,

vinay 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi Emerson,

The issue is likely due to the very small load attached to the UPS. In order for a calibration to perform meaningful results, the attached load should be greater than 30%. I would increase the load attached to the UPS to get the units up over 30%, then run the calibration again. It will still be difficult for the unit to display truly accurate runtimes when you reduce the load back to normal, but they will be much closer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Thanks for the feedback

Yes, when we did the calibration we used a 30% load.

The load currently displayed is what is actually being used in the nobreaks. Each nobreak has a server connected to it of the same model as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

About your only option at this point would be to try an additional calibration (with 30+% load). 

The batteries installed in your units have been in service long enough at this point that they have some wear & tear on them. If the batteries were brand new we could try a force reset of the constants in the UPS. Doing that at this point would cause the UPS to over estimate the runtime available which would result in some unexpected behavior.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Ok Liam I got it.

Since I had already done the calibration, I will leave it the way it is.

Another doubt, in this nobreak I'm using the APC9630 card and installed PCNS on the server I want to manage. How do I configure shutdown?

Today it looks like this:

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
2746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi Emerson,

Click on the Shutdown option for "UPS on battery" event and check on the box of "Enable Shutdown", now set the delay for the shutdown. It takes in seconds so you need to convert minutes to seconds and add it. Ex: to set the server to shutdown after 5 minutes of power outage I would multiply by 60 and set the delay as 300 seconds.

Regards,

vinay 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of