Lost the local network management interface-to-UPS communication.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Lost the local network management interface-to-UPS communication.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
7
14642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

Lost the local network management interface-to-UPS communication.

Model: SMX3000RMLV2U

I can log onto the interface of the card but from there all the screens display "Lost the local network management interface-to-UPS communication." at the top.

I've seen this isse in some other posts where the data.txt and event.txt were requested so I've included these.

I've just replaced the batteries on this unit but am still getting some beeps about twice a day. The panel on the front shows nothing. Would like to log in and see what is alerting me to.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

Hi,

1.) You physically remove the card from the UPS SmartSlot. It may have two screws securing it to the UPS on each side of its faceplate. Once the card is unsecured (if it was), you physically slide the card out, the LEDs will go out, and leave it off for 10-20 seconds. Then, push it back in after and after ~20-30 seconds, you should see some LEDs on the management card.

2.) Yes, documentation supporting that is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156132 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

To power cycle the card, you can also go to control->network->reset/reboot, or issue the "reboot" command via telnet, ssh or console port.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:06 PM

In your config.ini, it says "UPS Not Discovered" which agrees with the communication lost error you're seeing on the web interface. This could be a problem with either the management card (on its interface to the UPS) or with the UPS itself. I would tend to suspect the UPS, since you say that the front panel isn't displaying anything. It sounds like "nobody is home" in the UPS.

If your application allows this, I'd suggest powering down the equipment that is served by the UPS and then powering down the UPS and "dead-ing" it. Normally that is done by turning the UPS off at the front panel, unplugging it from its power source, and then pressing and holding the UPS power off button until you hear a beep and/or click and all of the LEDs on the UPS (including the back panel) turn off. That is the "classic" method to reset it - newer models like yours may have an alternate method.

Then plug the UPS back in and turn it on (before powering the connected equipment back on). Hopefully the UPS will wake up and display something on the front panel. If this was a one-time hiccup and the UPS is now working properly, you're all set. However, the UPS might not power back up, or it might come up but develop this same fault (or a different fault) after some period of time. In that case, you'd be looking at either a warranty repair/replacement or a non-warranty repair by CoastTec (assuming you're in the US) or replacement.

In either case, once you get the UPS going again, you may want to update the management card firmware - your config.ini says you're running 5.1.7 and the current version is 6.2.1 from here. Note that some configuration settings may not be retained because there are a number of changes between those two releases. You can compart the old config.ini file to the new one after updating to see what you might need to re-configure. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:06 PM

Yes, I agree with Terry. I'd also clarify what you mean by the UPS front panel not showing anything? No LEDs, no text, or is not showing anything related to this issue but appears normal?

If you just replaced the batteries, you need to do a UPS self test to clear the replace battery alarm. This typically can be executed from the panel if it was/is working normally.

Your management card can't "talk" to your UPS though is what it is trying to tell you and per your event log, it looks like this has been happening for some time. Terry mentioned some steps to try. You could also try rebooting your Management Card or power cycling it before what he suggested as some easier steps. Preferably, I'd recommend removing it from the UPS for 10-20 seconds and then re-inserting it and logging in and checking again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

On 6/1/2015 6:30 AM, Angela said:

I'd also clarify what you mean by the UPS front panel not showing anything?

Not showing anything related to this issue but appears normal.

I have done the Self Test (passed)

I would like to try rebooting the Management Card or power cycling before I shut down the entire UPS as it is in a production environment.

On 6/1/2015 6:30 AM, Angela said:

Preferably, I'd recommend removing it from the UPS for 10-20 seconds and then re-inserting it and logging in and checking again.

1. How do I cycle the power on just the card?

2. Can I remove/reinsert the card without shutting down the entire unit first?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

Hi,

1.) You physically remove the card from the UPS SmartSlot. It may have two screws securing it to the UPS on each side of its faceplate. Once the card is unsecured (if it was), you physically slide the card out, the LEDs will go out, and leave it off for 10-20 seconds. Then, push it back in after and after ~20-30 seconds, you should see some LEDs on the management card.

2.) Yes, documentation supporting that is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156132 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

To power cycle the card, you can also go to control->network->reset/reboot, or issue the "reboot" command via telnet, ssh or console port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

On 6/1/2015 11:40 AM, voidstar said:

To power cycle the card, you can also go to control->network->reset/reboot

I have no Network under Control - just UPS and Outlet groups

On 6/1/2015 11:40 AM, voidstar said:

or issue the "reboot" command via telnet, ssh or console port.

Success!! Card is back online.

Thanks to everyone for the prompt courteous help

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

0 Likes
0
14639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:41 AM . Last Modified: ‎2024-02-29 11:06 PM

For anyone else that finds this thread, I had the same issue and it happened all of a sudden in the middle of the night.

I tried restarting everything, reseating the card, nothing seemed to work.

I then pulled the card out and was going to let it sit for a few minutes to discharge but while looking at it I noticed a component wasn't attached to the circuit board, it was dangling loose from it's other terminal.

I believe it came loose due to a cold solder joint. This does happen in electronics. I pulled out my soldering iron and re-soldered the component to the board, reinstalled the card into the UPS and it is now working fine.

So, if re-seating, rebooting, restarting doesn't work check the board for any loose or damaged components. Either RMA if under warranty, if not under warranty then you can try re-solding the component but just remember you do this at your own risk. Remember that any modifications to a component under warranty voids the warranty and if improperly done you could cause irreversible damage to a already damaged product.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now