Load on battery during AVR boost

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Load on battery during AVR boost
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
eeolson_apc
eeolson_apc
Cadet

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

0 Likes
1
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

Load on battery during AVR boost

When a UPS is indicating AVR boost for undervoltage, is it drawing from the battery to make up for it? We have a UPS which stays in AVR boost state for extended periods, and would like to know if the battery is being hit during these times.

Also, if anyone can point to an APC white paper or something on how the AVR works, let me know...

thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • avr
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

hi-

the boost and trim functions do not use the battery. they use an internal transformer. if your UPS is in constant boost, even though it doesnt draw from the battery, you probably want to see if you can figure out what the issue is. constant use of the transformer heats up the UPS and in the long term, could shorten the life of the battery or the UPS. boost or trim isnt meant to be on 24/7. check your incoming voltage to see whats going on.

in regards to more info on AVR, check this thread: https://community.exchange.se.com/t5/Datacenter-Forum/bd-p/datacenter-forum

there are some helpful posts.

[this link|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=715] is from our knowledge base and can tell you when the AVR boost or trim will kick in (at which voltages).

i cant find any white papers or anything but essentually, the UPS boosts or trims the voltage accordingly for undervoltages or overvoltages by percentage. i believe the percentage is 12% and some have a double boost of 24%. it takes this percentage from the input voltage.

hope this helps. if i find anything else, i'll post it as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:09 AM . Last Modified: ‎2024-03-08 03:10 AM

hi-

the boost and trim functions do not use the battery. they use an internal transformer. if your UPS is in constant boost, even though it doesnt draw from the battery, you probably want to see if you can figure out what the issue is. constant use of the transformer heats up the UPS and in the long term, could shorten the life of the battery or the UPS. boost or trim isnt meant to be on 24/7. check your incoming voltage to see whats going on.

in regards to more info on AVR, check this thread: https://community.exchange.se.com/t5/Datacenter-Forum/bd-p/datacenter-forum

there are some helpful posts.

[this link|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=715] is from our knowledge base and can tell you when the AVR boost or trim will kick in (at which voltages).

i cant find any white papers or anything but essentually, the UPS boosts or trims the voltage accordingly for undervoltages or overvoltages by percentage. i believe the percentage is 12% and some have a double boost of 24%. it takes this percentage from the input voltage.

hope this helps. if i find anything else, i'll post it as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of