Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82563members
350177posts

Is this battery new and healthy?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
rotti_apc
Lieutenant JG
Lieutenant JG
0 Likes
1
209

Is this battery new and healthy?

This was originally posted on APC forums on 8/3/2020


I bought a new RBC7 battery replacement (17Ah, 24V) pack for a Smart-UPS SMT1500I (1500AV, 1050W) with a AP9631 Network Management Card 2. The NMC2 allows me to collect and plot data provided by the UPS.

So I ran tests: the load is a laptop charger and a traditional light bulb and the powerstrip with power monitor says together they peak at 150W.

1) disconnect the input power from the UPS (see attached picture SMT1500i-RBC7-batt)

2) built-in calibration test (see attached picture SMT1500i-RBC7-cal)

Both diagrams clearly show a 20% battery charge drop right when the UPS switches to battery output. After that drop the battery charge decreases linearly.

Is this normal behaviour of a new and freshly charged RBC7 model battery? If that is normal how is the initial charge drop explained?

 

 

Attachments

Accepted Solutions
rotti_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
209

Re: Is this battery new and healthy?

This was originally posted on APC forums on 8/3/2020


The battery charge reported by the UPS actually dropped as follows:

in test (1): 20%

in test (2): 40%

 

See Answer In Context

1 Reply 1
rotti_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
210

Re: Is this battery new and healthy?

This was originally posted on APC forums on 8/3/2020


The battery charge reported by the UPS actually dropped as follows:

in test (1): 20%