Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 07:03 AM . Last Modified: 2024-03-04 11:05 PM
Hello: We are trying to remotely change the state (Standby and ON) of 2 RP CW systems using the Input relay. The issue is that the unit request a "normal" state. So when we shutdown the system, the unit generates an alarm. but if we do change the normal status to closed, then when the unit is on, it considers this wrong and also generates an alarm. Any suggestions how to perform this remote ON/Stand by management?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 07:04 AM . Last Modified: 2024-03-04 11:05 PM
Hello.
The input is used for the remote power off (rpo) on this unit. It will always throw an alarm, when it is not in it's normal state. Unfortunately there is no way to stop it from alarming. We can turn off emails and stop it from logging these alarms through the web interface. This is under General then Notification then you will need to go to the specific alarm and turn off the logging and email. This is also the only way to remotely turn on and off the unit, short of cutting the input power to the unit.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 07:04 AM . Last Modified: 2024-03-04 11:05 PM
Hello.
The input is used for the remote power off (rpo) on this unit. It will always throw an alarm, when it is not in it's normal state. Unfortunately there is no way to stop it from alarming. We can turn off emails and stop it from logging these alarms through the web interface. This is under General then Notification then you will need to go to the specific alarm and turn off the logging and email. This is also the only way to remotely turn on and off the unit, short of cutting the input power to the unit.
Thank you