Input Voltage Or Frequency Cannot Support Bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
842

Input Voltage Or Frequency Cannot Support Bypass

This question was originally posted by Christian on APC forums on 2/24/2012


We've recently got our Smart-UPS RT 20000 RM XL hard-wired by our facility management. At first we had error messages that there are no batteries attached, which disappeared after a couple of hours. Our initial tests seem to indicate that everything else seems to work. I've connected a device to the UPS and it got power, the batteries show as connected and fully powered.

We still have the follow error message:

Input Voltage Or Frequency Cannot Support Bypass
UPS: An input voltage or frequency problem prevents switching to bypass mode.

I've attached screenshots of the status and about screens and the eventlog. I have no clue where to go from here. Is the UPS wired wrong or do we have to change a setting somewhere?

Any piece of advice is greatly appreciated.

Tags (2)

Accepted Solutions
upsguy_apc
Commander
Commander
0 Likes
0
842

Re: Input Voltage Or Frequency Cannot Support Bypass

This was originally posted on APC forums on 3/2/2012


Looks like you have no input to the bypass. If the unit is set up as single input and the jumpers aren't installed you'll have the issues your describing. You can see if your screen shot that the bypass voltage is 0.4V

http://www.apcmedia.com/salestools/ASTE-6Z8LVM_R1_EN.pdf

Pg 9 shows the input wiring configurations for single or dual input.

See Answer In Context

BillP
Administrator Administrator
Administrator
0 Likes
0
842

Re: Input Voltage Or Frequency Cannot Support Bypass

This reply was originally posted by Christian on APC forums on 3/5/2012


That's what I was afraid of - thanks for the answer.

See Answer In Context

2 Replies 2
upsguy_apc
Commander
Commander
0 Likes
0
843

Re: Input Voltage Or Frequency Cannot Support Bypass

This was originally posted on APC forums on 3/2/2012


Looks like you have no input to the bypass. If the unit is set up as single input and the jumpers aren't installed you'll have the issues your describing. You can see if your screen shot that the bypass voltage is 0.4V

http://www.apcmedia.com/salestools/ASTE-6Z8LVM_R1_EN.pdf

Pg 9 shows the input wiring configurations for single or dual input.

BillP
Administrator Administrator
Administrator
0 Likes
0
843

Re: Input Voltage Or Frequency Cannot Support Bypass

This reply was originally posted by Christian on APC forums on 3/5/2012


That's what I was afraid of - thanks for the answer.