InRow Cooling with outside condensing Unit

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ethode_apc
Crewman
Crewman
0 Likes
1
133

InRow Cooling with outside condensing Unit

This was originally posted on APC forums on 4/11/2016


Most of the systems I've seen for Row based cooling having the compressor in the row unit and then outside condenser.  I've seen some other manufacturers that instead have a condensing unit and then the row based unit doesn't contain the compressor and has more fans for a higher kW cooling capacity ... Does APC have any in row unit thats use an outside condensing unit vs condenser?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
133

Re: InRow Cooling with outside condensing Unit

This reply was originally posted by L2SupportServices-Cooling on APC forums on 4/11/2016


Hello Joshua. All of our air cooled (DX) units have the compressor inside the indoor unit. We do not have any units with the compressor in the condenser. The closest thing we would have to this is the chilled water units, that require a chiller unit outside that contains the compressor.

Thank you

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
134

Re: InRow Cooling with outside condensing Unit

This reply was originally posted by L2SupportServices-Cooling on APC forums on 4/11/2016


Hello Joshua. All of our air cooled (DX) units have the compressor inside the indoor unit. We do not have any units with the compressor in the condenser. The closest thing we would have to this is the chilled water units, that require a chiller unit outside that contains the compressor.

Thank you