Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82510members
350114posts

ISX PDU OID requirements

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
100

ISX PDU OID requirements

This question was originally posted by s on APC forums on 5/9/2008


I have got an ISX PDU that appears to have the latest xpdu image (v331) on its management card. I had a look through the PowerNet MIB and found an interesting OID...

.1.3.6.1.4.1.318.1.1.15.4.2.3.1.5
...enterprises.apc.products.hardware.xPDU.xPDUCircuitBreakers.xPDUBranchBreakers.xPDUBranchBreakerTable.xPDUBranchBreakerEntry.xPDUBranchBreakerCurrent

Which suggests it is a measurement of current drawn over each circuit.... however when polled on the device the results are all "-1", and as indicated in the MIB this is because the data is 'not available'.

the following specs may be reliant:

ISX PDU
Model: 0M-5402
Revision: B2
44 breakers installed.


Does anyone know what the requirements are to enable this monitoring? Hardware upgrade? software upgrade to intelligence module ('brain can'?) or a separate product?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: ISX PDU OID requirements

This reply was originally posted by Matt on APC forums on 5/9/2008


Shaynes,

You need to have the Branch Circuit Monitoring option installed in your PDU to enable current measurement on each breaker.
Generally this is configured on the initial design and installed at the factory. It's probably possible to install after the fact, but it's certainly going to require a shutdown.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: ISX PDU OID requirements

This reply was originally posted by s on APC forums on 5/12/2008


Is this something that can be installed by a fairly proficient end user, or does it require an APC engineer with part P certification etc?

BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: ISX PDU OID requirements

This reply was originally posted by Matt on APC forums on 5/9/2008


Shaynes,

You need to have the Branch Circuit Monitoring option installed in your PDU to enable current measurement on each breaker.
Generally this is configured on the initial design and installed at the factory. It's probably possible to install after the fact, but it's certainly going to require a shutdown.

BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: ISX PDU OID requirements

This reply was originally posted by Matt on APC forums on 5/15/2008


Shaynes,

I don't know all the steps for installing and configuring the Branch Circuit Monitoring option. Essentially what you get is a series of toroid current transformers that mount such that the circuit conductor passes through the transformer before it enters the breaker. Each set of 21 transformers has a sensing board that feeds into the intelligence module. (4 boards, one for each side of each distribution panel). I suspect the intelligence module needs to be configured to tell it that it now has the Branch Circuit Monitoring option. I don't know how to do this, or even if it's needed.