Galaxy 3000 charger fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Lhfelice_apc
Cadet
0 Likes
2
206

Galaxy 3000 charger fault

This was originally posted on APC forums on 4/14/2017


Hello all,

We have a galaxy 3000 ups that after a restart return charger fault and the battery cb goes off after 5 to 10 seconds of the startup.

The batteries are fully charged, each one reads between 13.3 and 13.5, the whole group reads 320v.

Any idea I appreciate.

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
208

Re: Galaxy 3000 charger fault

This reply was originally posted by Bill on APC forums on 4/14/2017


Luis,

I asked our Galaxy support team and they replied 

Most likely he has an open battery or connection in his battery string.

They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
209

Re: Galaxy 3000 charger fault

This reply was originally posted by Bill on APC forums on 4/14/2017


Luis,

I asked our Galaxy support team and they replied 

Most likely he has an open battery or connection in his battery string.

They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.

scort_apc
Crewman
Crewman
0 Likes
0
209

Re: Galaxy 3000 charger fault

This was originally posted on APC forums on 5/24/2017


You need to measure the voltage of each battery separately, necessarily with a small load of 2-5 watts