Fuse blew in UPS power cable - tripping the circuit. Causes?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Fuse blew in UPS power cable - tripping the circuit. Causes?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:50 AM . Last Modified: ‎2024-03-13 01:19 AM

0 Likes
2
1863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:50 AM . Last Modified: ‎2024-03-13 01:19 AM

Fuse blew in UPS power cable - tripping the circuit. Causes?

Hello,

I have a Smart UPS 1500 (SMT1500I) that protects two servers/a switch/gateway router/WAP and PBX. It is not in any way overloaded (usage is sitting around 15%) and has a long run time. It has been in service for about 4 months with no issues in that time and has protected the hardware during several outages and overvoltages.

On Weds evening Powerchute notified me that there had been a loss of power at the site location and then 15 minutes later a shutdown of the two servers was initiated. This was fine as that's what I wanted it to do. Come the next morning everything was still off so I assumed there was a prolonged outage at the site. On investigation by the client, it appears that the main board trip switch for the comms room had been tripped - no other power in the building was off and there had been no power outage. Further investigation showed that the fuse had blown in the cable from the wall socket to the UPS (I am in the UK) and only after replacement and resetting the trip did the UPS start to charge up.

Everything is now working fine, but I am curious as to the reason for the blown fuse in the power cable? Could it be just "one of those things"?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:19 AM

0 Likes
0
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:19 AM

Thanks for your reply.

Yes, it is a C13/C14 type system: http://en.wikipedia.org/wiki/IEC_60320#C13.2FC14_coupler - C14 (male) on rear of UPS, C13 (female) at the one end of the cable supplied by APC. At the wall socket, the cable has a UK plug (BS1363) incorporating a fuse (seems we're about the only ones to do this) - in this case the plug contained a 10amp fuse (as supplied by APC), which apparently blew.

I haven't seen this myself as I am remote from the system - the client stated this is what happened and the UPS only started to re-charge when she swapped the C13 > BS1363 cable for another identical one (we have plenty around as PCs use them as well).

It is all very odd... I can only think, like you, that something shorted out, but everything is back up working again without issue (all the hardware is 4 months old).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:50 AM . Last Modified: ‎2024-03-13 01:19 AM

0 Likes
0
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:50 AM . Last Modified: ‎2024-03-13 01:19 AM

i would make sure that none of your attached equipment has a short or similar.

also, I know this UPS has a C13 input connection? what type of power cord is this? (forgive me as I am based in NAM and I am only really familiar with C13-C14 for 230v or C13 to NEMA 5-15 for 120v domestic applications here).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:19 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:19 AM

Thanks for your reply.

Yes, it is a C13/C14 type system: http://en.wikipedia.org/wiki/IEC_60320#C13.2FC14_coupler - C14 (male) on rear of UPS, C13 (female) at the one end of the cable supplied by APC. At the wall socket, the cable has a UK plug (BS1363) incorporating a fuse (seems we're about the only ones to do this) - in this case the plug contained a 10amp fuse (as supplied by APC), which apparently blew.

I haven't seen this myself as I am remote from the system - the client stated this is what happened and the UPS only started to re-charge when she swapped the C13 > BS1363 cable for another identical one (we have plenty around as PCs use them as well).

It is all very odd... I can only think, like you, that something shorted out, but everything is back up working again without issue (all the hardware is 4 months old).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of