Duration of Shutdown and End of Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Duration of Shutdown and End of Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
2
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Duration of Shutdown and End of Shutdown

Can someone tell me on a network management card what the settings under Duration of Shutdown and End of Shutdown (Minimum Battery Capacity and Return Delay) mean. Also do these affect any of the other settings?

Thanks for your help

-Mark

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Minimum Battery Capacity and Return Delay refer to how quickly the unit will return to online after shutting down and going to sleep mode after a power outage. If you set the return capacity to say 50%, the battery will have to charge to 50% before it come back online. The same concept applies for the return delay setting.

The help file if you click it in the top right while logged into the interface explains every option pretty well. I'd suggest just checking there for most questions regarding configuration.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Yeah Mark I can help you out with those,

Minimum Battery Capacity is how much the ups will charge the battery before turning back on after a power failure. Depending on your available settings, you may want to set this so that if you have subsequent power outages, the ups is guarenteed to have enough runtime to gracefully shut your equipment down again.

Return Delay is how long the ups will wait after a power failure, after a scheduled shutdown, or after a shutdown initiated by a Control command to turn back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Minimum Battery Capacity and Return Delay refer to how quickly the unit will return to online after shutting down and going to sleep mode after a power outage. If you set the return capacity to say 50%, the battery will have to charge to 50% before it come back online. The same concept applies for the return delay setting.

The help file if you click it in the top right while logged into the interface explains every option pretty well. I'd suggest just checking there for most questions regarding configuration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of