If I am on the same subnet as the UPS/Card I am able to access the Telnet and HTTP servers on the Network Management Card. However, if I am sitting on another subnet, I am unable to access the servers. I am still able to ping the device, which shows the IP configuration is correct. I am wondering if there is a filter and/or security setting I am missing that will allow me access?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:05 AM . Last Modified: 3 weeks ago
There is not any type of ip filter you can set up for http or telnet access. I would verify with your network admin that ports 80, 443, or whatever other port you may have set in network settings of the card, are open between network segments.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:05 AM . Last Modified: 3 weeks ago
There is not any type of ip filter you can set up for http or telnet access. I would verify with your network admin that ports 80, 443, or whatever other port you may have set in network settings of the card, are open between network segments.