Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
rhyds_apc
Crewman
Crewman
0 Likes
1
146

Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS

This was originally posted on APC forums on 7/10/2012


I have a SmartUPS 1500 SUA1500I running both a windows server 2003 box (powerchute 8.0.1.609 connected by USB) and a telephone switch (not connected to UPS management, only running from the power output)

I wish to configure the UPS to run as normal for 15 minutes. After this i wish the server to be shut down but the UPS to remain active until its battery is depleted. How do I configure this in powerchute?

Message was edited by: rhyds

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
146

Re: Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS

This reply was originally posted by Bernard on APC forums on 7/10/2012


Good day rhyds,I suggest that you use Powerchute Network Shutdown (works with a network management card installed in the UPS) instead of Powerchute Business Edition. Because with PCBE, the UPS is commanded to go to low voltage sleep mode after the server gracefully shuts down.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
147

Re: Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS

This reply was originally posted by Bernard on APC forums on 7/10/2012


Good day rhyds,I suggest that you use Powerchute Network Shutdown (works with a network management card installed in the UPS) instead of Powerchute Business Edition. Because with PCBE, the UPS is commanded to go to low voltage sleep mode after the server gracefully shuts down.