Conected to the AP9630 card but no UPS/APC visible

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
sysapc_apc
Cadet
0 Likes
4
165

Conected to the AP9630 card but no UPS/APC visible

This was originally posted on APC forums on 10/5/2016


Hello everyone,

after upgrading the AP9630 firmware my UPS/APC smart 3000VA is not visible anymore,

i can reach the card but the card don't see the APC anymore.

it was the case before the update.

Am i missing something?

(screenshot)

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
165

Re: Conected to the AP9630 card but no UPS/APC visible

This reply was originally posted by Angela on APC forums on 10/5/2016


Thanks cool

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
165

Re: Conected to the AP9630 card but no UPS/APC visible

This reply was originally posted by Angela on APC forums on 10/5/2016


Hi,

Could you do a screenshot of the About->Network web page please? That will show us what firmware you have loaded. If you accidentally loaded the incorrect firmware application (such as for a different model of UPS), you could see this problem If that is the case, you can just reload the correct one which I can guide you to. If the firmware is correct, there are a few other steps we can try but incorrect firmware is the cause majority of the time.

sysapc_apc
Cadet
0 Likes
0
165

Re: Conected to the AP9630 card but no UPS/APC visible

This was originally posted on APC forums on 10/5/2016


Thank you Angela.

Screenshot in this message !

Attachments
sysapc_apc
Cadet
0 Likes
0
165

Re: Conected to the AP9630 card but no UPS/APC visible

This was originally posted on APC forums on 10/5/2016


Awesome Angela, YOU ROCKS!!!   🙂

BillP
Administrator Administrator
Administrator
0 Likes
0
166

Re: Conected to the AP9630 card but no UPS/APC visible

This reply was originally posted by Angela on APC forums on 10/5/2016


Thanks cool