Can't get humidity- and temp-value via SNMP

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
CWempe_apc
Crewman
Crewman
0 Likes
20
1694

Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/23/2010


I tried to read the value for relative humidity via SNMP.

Card: AP9631
Sensor: AP9335TH
Port: 2 (right; next to LAN)
SNMP-OID: .1.3.6.1.4.1.318.1.1.10.2.3.2.1.6.1 (humidity)

{color:#008000}The WebUI shows the correct values for temp and humidity!{color}
{color:#ff0000}But the SNMP-values are like "-1" or something.{color}

{color:#008000}Everything works fine if I connect the sensor to the first (left) port!{color}

{color:#ff6600}Another "problem" is that I have to reboot the NMC after connecting a sensor to another port.
{color}{color:#000000}
Can anybody approve or disprove this behaviour?
{color}

Message was edited by: CWempe

Message was edited by: CWempe


Accepted Solutions
bbiandov_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 10/31/2019


In my case the OID was .1.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1 for the external temperature probe for RT5000 with AP9537SUM 

 

Qn74k%2BdD%2FxSgURibayopHg%3D%3D.png

See Answer In Context

Attachments
20 Replies 20
alanth_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 5/10/2013


Jon P.

You state that "SNMP-OID: .1.3.6.1.4.1.318.1.1.25.1.2.1.6 (The sensor's current temperature reading in tenths of degrees Celsius.)"

However, the output is an INTEGER which is always in WHOLE number degrees, not tenths of degrees!

How to I change the output to tenths of degrees?

snmpwalk [hostname] -v1 -c public .1.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1

SNMPv2-SMI::enterprises.318.1.1.25.1.2.1.6.1.1 = INTEGER: 25


BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 5/10/2013


let me look into this one..i see what you're saying - i'll report back but if it is an issue, we'll have to address it in the next firmware rev unless your tool can at least append a .0 within your tool which doesnt look like it if you're using a CLI SNMP tool.

alanth_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 5/10/2013


After a further bit of research, it seems that there is no support for non-integer values (floating-point) in the SNMP standard itself.

Netbotz outputs the value as rounded INTEGER & STRING but those OIDs don't work for APC 9631:

.enterprises.5528.100.4.1.1.1.7.1095346743 = STRING: "16.800000"

.enterprises.5528.100.4.1.1.1.8.1095346743 = INTEGER: 16

.enterprises.5528.100.4.1.1.1.9.1095346743 = INTEGER: 62

Other products output the value in actual tenths of degrees (i.e. 25.7 deg = INTEGER: 257)

This is what seems to be advertised, but is not the case in FW ver. 5.1.7

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 5/13/2013


I went ahead and logged an issue against it for both tempC and tempF as well as humidity. It also exists in our newest version of 6.0.6.

alanth_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 5/14/2013


Thank you - while you (the corporate you) are at it, maybe we could get hundredths of degrees? smile

magalhaes_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/13/2014


Hi all!

My AP9631 OID list, got by snmpwalk,  goes untill  .1.3.6.1.2.1.33.1.9.10.0. In this way, I can not get temperature values also.


What can I do to get the rest of OIDs?

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 11/13/2014


You'll want to download the APC PowerNet MIB and load/compile it into your system to get the APC specific OIDs. You'll find it here -> http://www.apc.com/tools/download/index.cfm and look for Firmware Upgrades - MIB on the Filter by Software/Firmware drop down list.

magalhaes_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/13/2014


Angela,

Thanks for your replay.

I follow you tip and my APC model is not in the compatible modes list. I have an APC SURT6000XLI.

It´s possible to use the firmware without problem?

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 11/13/2014


I'm not sure what you're looking at.

If your UPS (SURT6000XLI) has a Network Management Card installed (AP9617/18/19 or AP9630/31), then you can use SNMP with it. To use SNMP, you need the SNMP MIB with all of the APC specific OIDs. That is what I was suggesting you download into your SNMP tool. You don't need to likely touch the SURT6000XLI at all. The MIB does not have a compatibility list so that is why I was not sure what you were referring to.

magalhaes_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/14/2014


Ok. I´ll explain.

You said:  "You'll want to download the APC PowerNet MIB and load/compile it into your system to get the APC specific OIDs. You'll find it here -> http://www.apc.com/tools/download/index.cfm and look for Firmware Upgrades - MIB on the Filter by Software/Firmware drop down list."


Then, I did it as you told me. When I looked for Firmware Upgrades - MIB on the download page I was redirected to firmware updates download page where there are two itens: PowerNet MIB v4.1.2 (this one has a compatible hardware list) and NetBotz MIB v3.0.0.


By clicking on  PowerNet MIB v4.1.2 compatible hardware list, my UPS model is not listed.

So, my doubt now is: If I apply this firmware update, could I have any trouble? Do you understand now?

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 11/14/2014


Yes, I do, thanks for the clarification.

The compatibility list for PowerNet MIB is misleading. You don't need to worry about that. What I wanted you to download is that file, PowerNet MIB 4.1.2 and that works with AP9617/18/19 or AP9630/31 which is the actual Network Management Card that is installed in your UPS and provides the Network Interface and SNMP functionality. What I am telling you is to not worry about the compatibility because I can assure you the v4.1.2 MIB will work and is what you need. smile It covers every APC product besides NetBotz and that is why there is a separate MIB for those. And the MIB won't work with SURT6000XLI so that is why it is likely not listed because it works with the actual Network Management Card itself as I noted.

Hope that helps. Let me know if you still have any troubles downloading it or anything.

magalhaes_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/14/2014


My last question. How can i load de .mib file into the Network Management Card? Is there an apllication? By command line?

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 11/14/2014


You don't load it onto the management card. You need to load it into your SNMP tool that you use to gather data from the Network Management Card. You may need to find out for your SNMP tool how to load a MIB so that you can browse the APC OIDs.

kyoshimura_apc
Cadet
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 6/5/2013


i have (near) same problem.

AP9631 & AP9335TH

SNMP OID:

(humidity) .1.3.6.1.4.1.318.1.1.25.1.2.1.7.1.1

(temprature) .1.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1

I have get tempurature value from this, but can't get humidity value. But by snmpwalk, get humidity value.

why?

-------------

****@debian1:~$ snmpwalk -v 1 -c public AAA.AAA.AAA.AAA .1.3.6.1.4.1.318.1.1.25.1

iso.3.6.1.4.1.318.1.1.25.1.1.0 = INTEGER: 2

iso.3.6.1.4.1.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1

iso.3.6.1.4.1.318.1.1.25.1.2.1.1.2.1 = INTEGER: 2

iso.3.6.1.4.1.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1

iso.3.6.1.4.1.318.1.1.25.1.2.1.2.2.1 = INTEGER: 1

iso.3.6.1.4.1.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1"

iso.3.6.1.4.1.318.1.1.25.1.2.1.3.2.1 = STRING: "Port 2 Temp 2"

iso.3.6.1.4.1.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1"

iso.3.6.1.4.1.318.1.1.25.1.2.1.4.2.1 = STRING: "Port 2"

iso.3.6.1.4.1.318.1.1.25.1.2.1.5.1.1 = INTEGER: 77

iso.3.6.1.4.1.318.1.1.25.1.2.1.5.2.1 = INTEGER: 77

iso.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1 = INTEGER: 25

iso.3.6.1.4.1.318.1.1.25.1.2.1.6.2.1 = INTEGER: 25

iso.3.6.1.4.1.318.1.1.25.1.2.1.7.1.1 = INTEGER: 44

iso.3.6.1.4.1.318.1.1.25.1.2.1.7.2.1 = INTEGER: -1

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 6/5/2013


I'm not sure what you mean - when you GET a single OID for humidity, it doesn't work but if you do a walk you see it? I only have an AP9335T temp sensor but either if I walk it or I just GET that one OID, I am seeing a response of -1 indicating it's not supported.

Also, what firmware version is on your AP9631 please?

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Angela on APC forums on 5/14/2013


I am not sure if the probe is capable of that to be honest, lol

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Jonathan on APC forums on 11/23/2010


If you are usisng an AP9631 and it is attached to a UPS i.e. Smart-UPS you can try the following OID.

SNMP-OID: .1.3.6.1.4.1.318.1.1.25.1.2.1.5 (The sensor's current temperature reading in tenths of degrees Fahrenheit.)
SNMP-OID: .1.3.6.1.4.1.318.1.1.25.1.2.1.6 (The sensor's current temperature reading in tenths of degrees Celsius.)
SNMP-OID: .1.3.6.1.4.1.318.1.1.25.1.2.1.7 (The current humidity reading in tenths of percent from the sensor.)

An updated APC MIB file can also be downloaded here http://www.apc.com/tools/download/index.cfm, on the Filter by Software / Firmware Box choose Firmware Upgrades - MIB.

CWempe_apc
Crewman
Crewman
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 11/24/2010


Thanks.

I didn't knew this universalInputOutput tree.

I will try if this "fixes" my problem.

BillP
Administrator Administrator
Administrator
0 Likes
0
1694

Re: Can't get humidity- and temp-value via SNMP

This reply was originally posted by Jonathan on APC forums on 11/24/2010


The tree was introduced to accomodate the latest NMC2 feature, if you were able to download the latest MIB file it should show up.

bbiandov_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
1695

Re: Can't get humidity- and temp-value via SNMP

This was originally posted on APC forums on 10/31/2019


In my case the OID was .1.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1 for the external temperature probe for RT5000 with AP9537SUM 

 

Qn74k%2BdD%2FxSgURibayopHg%3D%3D.png