Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Can't connect Smart UPS 700 (SU700NET) via serial port

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't connect Smart UPS 700 (SU700NET) via serial port
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
DennisTobi_apc
Crewman DennisTobi_apc
Crewman

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

0 Likes
4
1934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

Can't connect Smart UPS 700 (SU700NET) via serial port

Hello,

we have a Smart UPS connected with our company Server. It was installed by a service provider which we don't work with anymore.

I have seen that the load display doesn't show any light and I can't connect via Powerchute Software to the UPS. AS our server doesn't have a native serial port a PCIe-to-serial Addon card is installed. I updated the Powerchute Software to the latest available version (from 6.2 to 9.1.1) but nothing changed. I tried to check the serial port with putty (2400-8-1-none-XON/XOFF) but nothing happens.

Any suggestions what I could change in the serial settings to get a connection? Only during bootup the load display light, but after bootup nothing happens.

I will attach two screenshots of the available serial settings.

Thanks in advance.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DennisTobi_apc
Crewman DennisTobi_apc
Crewman

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
1928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:53 PM

Hi Bill,

yes I have set a new user and password during installation but unfortunately this won't work. Maybe I will reinstall again on the weekend and try again. During working time I can't restart the server often as our company is working with it.

I will give a feedback within the next days.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

0 Likes
0
1928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

Dennis,

Change the flow control to None and test that. The other thing to check is to verify that Com Port 2 is the one the UPS is attached to. You can test communication (as you mentioned) using PuTTY. Once PuTTY is configured for serial comm at the prompt type capital Y The UPS should responded with the letters SM. if it responds with SM that indicates that the UPS and OS are communicating.

Reply

Link copied. Please paste this link to share this article on your social media post.

DennisTobi_apc
Crewman DennisTobi_apc
Crewman

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

0 Likes
0
1928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

Hi Bill,

thanks for your reply. I can't get putty to work. But I found another programm called Termite, I tried the capitel Y at COM3 port and it responded SM like expected. (Attached screenshot).

Right now I can't add a device in the Device List Wizard. When I try to login to the agent via webinterface it asks for a Username and Password which I don't know. trying to figure out this issue now...

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

0 Likes
0
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

Dennis,

The user name and password are set when PowerChute is installed. Unfortunately there is no over ride so if you do not know the PowerChute user name and password you have to uninstall PowerChute and reinstall. Also, If you are installing the Agent, Server, and Console the user name and password must be the same for the Agent and Server or the Server will not discover the Agent.

Reply

Link copied. Please paste this link to share this article on your social media post.

DennisTobi_apc
Crewman DennisTobi_apc
Crewman

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
1929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:53 PM

Hi Bill,

yes I have set a new user and password during installation but unfortunately this won't work. Maybe I will reinstall again on the weekend and try again. During working time I can't restart the server often as our company is working with it.

I will give a feedback within the next days.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of