Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Can I run my SURTD5000XLI with only SURT192XLBP external battery pack?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Can I run my SURTD5000XLI with only SURT192XLBP external battery pack?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Hellrack_apc
Hellrack_apc
Cadet

Posted: ‎2021-06-30 01:43 AM

0 Likes
9
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

Can I run my SURTD5000XLI with only SURT192XLBP external battery pack?

This was originally posted on APC forums on 12/27/2011


Hi folks. Rbc44 cartridges of my SURTD5000XLI are dead so i'm going to replace them. Can I run my ups with only external battery pack? Is that possible?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
David.Harris_apc
Crewman David.Harris_apc
Crewman

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 2/26/2017


So following @psyfy's great post above, I wonder if this could extend to running a Tesla Powerwall 2 - or are there too much 'smarts' needed to charge this - am guessing you'd have to hack the interface too.

And obviously you'd need to have a substantial sized UPS to cater for its output, say 5kva or greater, because I believe the PowerWall is 5kva rated, but it certainly would take things to a whole new level.

The BlueSea 7610 Automatic Charging Relay on Amazon is $75 and caters for most of what is required, plus BlueSea have a bunch of circuits p13 through p49 of their catalog catering to dual battery charging and switching (I have no affiliation with them either, and its way overkill but great stuff)

BlueSea ACR

http://catalog.bluesea.com/files/assets/basic-html/page-40.html 

Am now very interested to try this out - I happen to have a large APC 'online' UPS with stuffed batteries from many years ago that I'll drag out of storage and begin adding the stage one circuitry and Anderson plugs and test out a couple of deep cycle batteries in series. Then if someone has Tesla feedback I might get really game and order one . . .

Will revert with feedback and pics.

@psyfy please PM me if you're still active online.

See Answer In Context

Attachments
  • Tags:
  • battery
  • charging
  • extended
  • external
  • powerwall
  • tesla
  • ups
Reply
Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This reply was originally posted by Chris on APC forums on 12/27/2011


Your best option would be to take the RBC44's out of the external and put them in your UPS. You can leave the others disconnected(the ups doesn't use as many batteries as the external battery pack does). To answer your question though, it will probably still work but just isn't a practical way to do it.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This reply was originally posted by Dakota on APC forums on 12/28/2011


leave The Battreries IN The External Pack The Ups Connects All Battery Packs In Paralell (Both Internal and External)

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This reply was originally posted by Chris on APC forums on 12/28/2011


There is no really benefit either way other than the fact that it prevents you from lifting the batteries of the external frame to the main.

Reply
PanMICRO_apc
Crewman PanMICRO_apc
Crewman

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 2/28/2013


Hi, yes indeed you can. I am somewhat of a hardware hacker and it took me a little while to figure out the 'goings on' with UPS's but I share these finding with you.

My own IBM10000XVH is connected in parallel to the two supplied external 150A Anderson connectors that are in turn fed by 24 x x2v 500Ah Supersafe VRLA cells.

Don't forget that 10000VA@48VDC will draw 200A DC and that momentary surge values are >= 240A+. Therefore you need to consider the size of the cable feeding the UPS inputs from the battery banks. Too small and they will get hot as the voltage drop will be too great at elevated loads.

I use 2 x 1 metre lengths of 35mm2 copper cable (150A per cable) to go from the batteries to the UPS and another two to return to the Batt(-). I decided to do this as I already had the 35mm2 cable but you could also use a single 70mm2 as the Andersons are paralleled at the UPS end anyway. You could also use a 6061T 125mm2 bussbar (25mmx6mm) to feed the UPS inputs, derated x 0.6 for the Alu.

You are correct about the duty cycle being 100% on a double conversion UPS and cooling is sufficient, though I would err on the side of caution when it came to elevated [loading:duty cycle] ratios. 50% is the usual rule of thumb when it comes to the compromise of design, cost and thermal shutdown. What I am saying is that I have not tested this, if you are able, stick 2 Temp probes on the unit and test. 1 on the bridge heatsink and the other on the step up transformer. Neither should go much beyond 70degC. Anyway, I digress.

Concerning battery charging? have a look at the MIB for your UPS. You note that there are SNMP traps for battery ampacity values settable from 1 - 2000Ah and the battery types are also settable. Naturally the default is for 'Gel' however, there are 5 other types of battery chemistry catered for including 'VRLA', which I am using.

Makes a wonderful upmarket DC-AC solar inverter.

Hope that this info helps you out...

Reply
TerryKennedy_apc
Lieutenant TerryKennedy_apc
Lieutenant

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 12/19/2012


I'm not really familiar with the newer models - mostly I deal with SU and SUA Smart-UPS and Matrix and older Symmetra units.

If the internal pack just uses a 2-pin battery connector, the UPS won't notice that it is missing. All of the battery packs are just bridged together in parallel (though the batteries inside each module are wired in series to create 48V, or 24V on some units). You'll probably want to keep the empty battery pack in the UPS as the design may depend on that space being occupied to provide proper airflow. You definitely want to remove the individual batteries as worn-out batteries tend to overheat and swell as the UPS keeps trying to charge them.

Reply
Bicka_apc
Bicka_apc
Cadet

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 12/19/2012


Can I run my SURT8000XLI off External Batteries only? I have the 4 of the RBC44 cartridges but theres no batteries inside. I was planning on building a custom pack of Lead Acid batteries for an extended run application (using deep cycle batteries).

I know this probably voids warranties and isn't supported.

I would just like a simple answer as to if this UPS will cold start from external batteries only, or will I have to wire the external pack through the Internal mounting point? where the cartridge plugs in.

Thanks.

Reply
TerryKennedy_apc
Lieutenant TerryKennedy_apc
Lieutenant

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 12/19/2012


I'm just another end user, so this certainly isn't a statement from APC. Having said that...

You can do this sort of thing with APC UPS's that support external battery modules but do not use a communication cable, just the positive and negative battery connections. These are generally the units that you have to tell how many external battery modules are connected. Matrix and Symmetra units (and probably some other models) use a communication cable which tells the UPS how many modules are connected, the state of charge on each, and so on. On those, unless you fake the data the UPS is expecting on that cable, it won't cold start.

You'll want to install fuse(s) of an appropriate rating in whatever sort of external battery pack you use. Other cautions would be that the UPS doesn't have an unlimited amp capacity for charging batteries (for example, a car battery on a Smart-UPS 750 won't get charged as the UPS can't supply enough charging current if the battery is discharged). Also, the UPS may not have been designed for continuous (or extended) run on batteries as the inverter components inside may overheat and trip a thermal safety. As an example, I believe the XR versions of the SUA1000 have a fan inside the UPS to keep the electronics cool, while the non-XR ones don't. If you limit yourself to a total Amp-Hour battery capacity that's equal to or less than the UPS with the maximum number of official APC battery modules, you'll probably have better reliability as that will be within both the charging and cooling ratings of the UPS.

Reply
Bicka_apc
Bicka_apc
Cadet

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 12/19/2012


Thanks alot for the quick response. The unit is Double Conversion online so I assume since its rectifying the AC Input to DC and the batteries would be supplying DC there would be no difference to the Inverter as it is constantly running on utility power anyway.
I suppose it will be if the unit can power on with the RBC44 cartridges missing... or "tricked" by supplying the external pack voltage in parallel. I was planning on getting batteries that are a multiple of the standard external packs (SURT192XLBP) these contain 4 RBC44 cartridges. 5Ah x 8 standard RBC44. The external pack can be made to contain 16 x 50Ah deep cycle batteries as it will be the same as connecting 5 SURT192XLBP external packs (4 x 8 x 5Ah). or 4 Externals and 1 Internal.

Thanks for your help. Hope you follow my logic.

This assumes that the unit will cold boot from an external pack only with no internal RBC44 cartridges installed or installed and not populated with batteries.

Reply
David.Harris_apc
Crewman David.Harris_apc
Crewman

Posted: ‎2021-06-30 01:43 AM

0 Likes
0
670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 01:43 AM

This was originally posted on APC forums on 2/26/2017


So following @psyfy's great post above, I wonder if this could extend to running a Tesla Powerwall 2 - or are there too much 'smarts' needed to charge this - am guessing you'd have to hack the interface too.

And obviously you'd need to have a substantial sized UPS to cater for its output, say 5kva or greater, because I believe the PowerWall is 5kva rated, but it certainly would take things to a whole new level.

The BlueSea 7610 Automatic Charging Relay on Amazon is $75 and caters for most of what is required, plus BlueSea have a bunch of circuits p13 through p49 of their catalog catering to dual battery charging and switching (I have no affiliation with them either, and its way overkill but great stuff)

BlueSea ACR

http://catalog.bluesea.com/files/assets/basic-html/page-40.html 

Am now very interested to try this out - I happen to have a large APC 'online' UPS with stuffed batteries from many years ago that I'll drag out of storage and begin adding the stage one circuitry and Anderson plugs and test out a couple of deep cycle batteries in series. Then if someone has Tesla feedback I might get really game and order one . . .

Will revert with feedback and pics.

@psyfy please PM me if you're still active online.

Attachments
  • Tags:
  • battery
  • charging
  • extended
  • external
  • powerwall
  • tesla
  • ups
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc