84579members
353849posts
Brand new Smart-UPS X 3000 showing errors /discharged battery
seanholmes_apc
142
This was originally posted on APC forums on 3/27/2017
 Critical Alarm Discharged Battery
The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
  Warning Alarm Overvoltage
Compensating for a high input voltage.
From status:
Status Smart-UPS X 3000
Last Battery Transfer: None
Internal Temperature: 74.44°F
Runtime Remaining: 0 minutes
UPS Input
Input Voltage: 218.09 VAC @59.97 Hz
UPS Output
Output Voltage: 208.78 VAC @59.97 Hz
Load Current: 4.62 Amps
Output VA: 32.20 %
Output Watts: 31.37 %
Battery Status
Battery Capacity: 0.00 %
Battery Voltage: 136.46 VDC
UPS is working, but battery doesn't seem to be getting a charge, not sure how to fix.
thanks
seanholmes_apc
Re: Brand new Smart-UPS X 3000 showing errors /discharged battery
This was originally posted on APC forums on 3/28/2017
it must have just been needing a good charge. Checked this morning and its "online' and green.
The unit was brand new to me, but must have been sitting in some stockroom for years. MFG on battery is 2014. Its charged 100% now though.
thanks
Sean
2 Replies 2
This reply was originally posted by Liam on APC forums on 3/28/2017
The float voltage of your battery is currently 136v, so it is definitely getting a charge. I see in your title that the unit is new. Do you have the serial number? Also - Have you adjusted the low battery signal time from the factory defaults?
seanholmes_apc
thanks
Sean