Battery calibration key / constant for Smart-Ups 1400 RM

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ocgltd_apc
Ensign
Ensign
0 Likes
1
237

Battery calibration key / constant for Smart-Ups 1400 RM

This was originally posted on APC forums on 8/7/2018


I put new batteries in my SU 1400 RM and discover that my UPS incorrectly shows batteries discharged after a a few minutes.  I found the EXACT same symptoms and cause and solution on the forums, and the solution was to enter a new constant for the batteries (calibration key)

I also found the instructions online for how to adjust the constant using a serial terminal.  Now I just need the value to set the constant to.

Could you post the battery constant / calibration key value I should use for the Smart-UPS 1400 RM ?


Accepted Solutions
voidstar_apc
Janeway
Janeway
0 Likes
0
237

Re: Battery calibration key / constant for Smart-Ups 1400 RM

This was originally posted on APC forums on 8/9/2018


You can do a manual calibration. Load the UPS to 30% or more (ie, 285W or more for your UPS), make sure the battery is charged 100%, unplug it, and let it run until it turns off.

See Answer In Context

1 Reply 1
voidstar_apc
Janeway
Janeway
0 Likes
0
238

Re: Battery calibration key / constant for Smart-Ups 1400 RM

This was originally posted on APC forums on 8/9/2018


You can do a manual calibration. Load the UPS to 30% or more (ie, 285W or more for your UPS), make sure the battery is charged 100%, unplug it, and let it run until it turns off.