Battery Constant for SU1400RMXLI3U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery Constant for SU1400RMXLI3U
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

0 Likes
5
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

Battery Constant for SU1400RMXLI3U

I need Battery Constanct value for UPS SU1400RMXLI3U 230v This is an old discountinued UPS. It is suddenly behaving wrong. Battery charging stopping at 72%, battery volts stopping at 25.98. I check in EEPROM for option b and it is showing firmware *73.14.I* which i belive is wrong. i belive 73.14.I is for SU1400 and Not for XL model. Also when i did SHIFT+V it displays KWI which i belive should be LWI. So what is correct battery constant values so i can correct my UPS? anyonw know?

According to http://www.apcupsd.com/manual/manual.html#resetting-the-ups-battery-constant SU1400RMXLI3U have 73.14.I but it is wrong. It must be someting different. Batteries are only 3 months old. Problem started suddenly. so i strongly belive that its something to do with battery constant. But unable to correct my problem. Any help is highly apreciated.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

I have a question for you. I have an old SU2200 manufactured in 1999 and the battery voltage will never get above 95% or 54.04 volts. Do you think the procedure you've found will reset the float voltage and work to put my battery voltage back to 100%?

Thanks for your thoughts!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

Hi I actually fixed my Smart-UPS with this procedure..hopefully it will help you

download apcfix.exe (google) you have to find it.. when you get to the page (yes it is in Russian) download the "newest version"

after installing

If you installed powerchute you must disable the service by going to CONTORL-ALT-DELETE start task manager under services tab, bottom click services, find APC PBE AGENT and stop the service..

When the service has been stopped then you open apcfix.exe and select the comm port ups is on..

it should open in a few seconds and make sure you model number is correct..

click options at the top..

click second option BATTERY CONSTANT FIX then CLOSE APCFIX.EXE

REOPEN APCFIX.EXE and you will here your unit being overwritten.. and the lights will stop flashing and battery constant will be fixed..

this helped me hope it will help you as well!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

You need to check multiple things. Try one by one and test if that works.
1. Set battery constant. My UPS have a problem that whenever it do auto TEST(scheduled monthly), it reset battery constant to wrong value, so i correct it on monthly bases. So first thing is correct battery constant.You can find your battery constant value at http://www.apcupsd.com/manual/manual.html#resetting-the-ups-battery-constant

your value will be something this depending upon your model:

SU2200XL,3000 35 EE FB AF

SUA2200I 08 B8 12 B3

SUA2200RMI2U 09 BC 11 81

SUA2200XLI 0A B7 0F 7F

2. Correct float volt. your float volt is little less. this could be a reason that ups stop charging at 95%. I belive that you are using 48v UPS so it should be 54.40 and not 54.04. For 24v UPS it should be 27.20.

Hopefully this will help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:42 AM

Thanks for the response.  I reset the battery constant to hex AF and also found some resistors (R38, R43, R118 and R119) in the charger circuitry had drifted out of tolerance.  I replaced the resistors and the float voltage is now back up and the UPS indicates 100% charge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

ok i am answering my own question. I set float volts to 27.20. and when battery charged. i shutoff ups. seprated beteries and then rejoin. and everything back to normal. Thanks everyone

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:37 PM . Last Modified: ‎2024-03-11 04:41 AM

I have a question for you. I have an old SU2200 manufactured in 1999 and the battery voltage will never get above 95% or 54.04 volts. Do you think the procedure you've found will reset the float voltage and work to put my battery voltage back to 100%?

Thanks for your thoughts!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of