Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Are Network Management Cards compatibles with Dell Smart-UPS ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Are Network Management Cards compatibles with Dell Smart-UPS ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
3
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Are Network Management Cards compatibles with Dell Smart-UPS ?

Hello,

I am facing a strange issue :
* AP9617 (w/ latest firmware) and AP9630 (brand new) are both working fine in an APC Smart-UPS 5000VA SUA5000RMI5U
* Same cards are not working at all (no LED light at all) in a Dell Smart-UPS 3000VA DLA3000RMI2U

I tried several time to reseat them in the Dell UPS, following the brain dead procedure... But it changed nothing.

Connected to the serial port of the Dell at 2400 8N1, I can confirm Smart Mode is enabled when typing shift-Y shift-A Enter...
I get the correct answers :
SM
OK
NA

So I am asking myself if APC NMC are compatible with APC UPS sold by Dell, or if I am facing an issue within the UPS (either hardware or software).

Unfortunately this UPS in not under warranty anymore.
I've read somewhere in the forum there may be some ribbon cable or connectors issue.
Is it worth opening the case to check connectivity ? Is there anything else to try ?

Thanks in advance for your help
Best regards
Fabrice

Message was edited by: fabsainte

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Hi fabsainte,

Network Management Cards 1 (AP9618/19/17) and 2 (AP9630/31) are compatible with Dell branded APC Smart-UPS. It almost has the same feature and functions as a regular APC Smart-UPS. While you are connected to the UPS using Hyper Terminal or PuTty, can you try pressing Shift+A? Make sure as well that the card is properly seated into the Dell Smart-UPS smart slot. The smart slot is where you install/slide in the card.

If properly done, the NMC LEDs should lit up in your case if the card LEDs does not lit up on this UPS but it does on another UPS there's a possibility that the smart slot is the culprit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Hi fabsainte,

Network Management Cards 1 (AP9618/19/17) and 2 (AP9630/31) are compatible with Dell branded APC Smart-UPS. It almost has the same feature and functions as a regular APC Smart-UPS. While you are connected to the UPS using Hyper Terminal or PuTty, can you try pressing Shift+A? Make sure as well that the card is properly seated into the Dell Smart-UPS smart slot. The smart slot is where you install/slide in the card.

If properly done, the NMC LEDs should lit up in your case if the card LEDs does not lit up on this UPS but it does on another UPS there's a possibility that the smart slot is the culprit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Hi,

Everything was fine from a Serial port point of view, but the management cards did not even light up their STATUS LED.
I has also a feeling that NMC was not being plugged when I was inserting it inside NMC slot (no resistance at all).

This morning, I fully stopped the UPS, removed the battery, unracked it, and then opened the case, removing the top cover.

It gave me quickly the confirmation that it was "only" an internal connectivity issue: the internal connector at the back of NMC slot was not full inserted !!!
So I just firmly pushed it inside its receptacle, closed everything, put back in rack... and now everything is fine !

Notice: opening the UPS should be only done by qualified technicians.

Regards
Fabrice

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

It is nice to know that you got it working. As a note as well, we do not recommend anyone to open and remove the top cover or casing of our UPS. The customer can only remove the battery door to install/remove the battery.

Opening the case of the UPS voids the warranty and pose a hazard of electrical shock.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of