Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
4
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

Application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' for acrc103

Hi

In telnet i have the error - Indicates that the application is not compatible with the AOS.' due to the 'Status : P+ N+ A!' and i can't access it on the web, only telnet, and the display of the unit it's blank, and no butons function.

I tried to uprgade the firmware, but the problem doesn't dissapear. The same if a made a downgrade of the firmware.

the unit is working, but because of this i suspect that one of the other 8 units from the group have alarm - lost group communication. If i cleare the alarm it appears after 15 sec, and if i shutdown the unit from the main supply, the alarm appears to another unit.

Pls help me to find an AOS that is compatible with the application.

Thanks in advanced.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

Hello.

     The ACRC103 unit needs the application section of the firmware loaded for it to work right. You will see P+N+A+ when it is loaded properly.I have included a link to our website, where you can download the 373 firmware which is the newest version. I have also included a link to our knowledge base. If you search for "FA156047", this will pull up a document that will walk you through the upgrade process (use the NMC 1 instructions). If you choose to use the serial (XModem) method there are 2 changes to the document. First use a null modem cable and second, it is 9600 bits per second not 2400.

     For the group communication alarm, if the unit that does not have the firmware loaded on it is in the group, then that is the cause of the group comm loss alarms. Getting the firmware on the unit so it is seen by the group again will cause the group comm loss alarms to clear. If you need any help upgrading the firmware you can call into our tech support lines (North America 888-695-6500 opt 2) and we can help you through the firmware upgrade.

Thank you

FAQ

InRow RC, 300mm, Chilled Water, 100-120V, 50/60 Hz - Download Software and Firmware | APC

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

Hello.

     The ACRC103 unit needs the application section of the firmware loaded for it to work right. You will see P+N+A+ when it is loaded properly.I have included a link to our website, where you can download the 373 firmware which is the newest version. I have also included a link to our knowledge base. If you search for "FA156047", this will pull up a document that will walk you through the upgrade process (use the NMC 1 instructions). If you choose to use the serial (XModem) method there are 2 changes to the document. First use a null modem cable and second, it is 9600 bits per second not 2400.

     For the group communication alarm, if the unit that does not have the firmware loaded on it is in the group, then that is the cause of the group comm loss alarms. Getting the firmware on the unit so it is seen by the group again will cause the group comm loss alarms to clear. If you need any help upgrading the firmware you can call into our tech support lines (North America 888-695-6500 opt 2) and we can help you through the firmware upgrade.

Thank you

FAQ

InRow RC, 300mm, Chilled Water, 100-120V, 50/60 Hz - Download Software and Firmware | APC

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

Since it appears your in the EMEA region, you can use http://www.apc.com/support/contact/index.cfm to contact technical support for your region if the steps above do not work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:55 AM

0 Likes
0
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:55 AM

Thank you for the fast answer, i did what you tell me, but after downloading the 3.7.3 firmware application and run it, i have the same status and the same problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:55 AM

0 Likes
0
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:55 AM

Hello.

If this is the case then the application is not loading properly. If you are just using the executable file to try and upload the firmware, try the ftp or XModem.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of