Another PCNS/Shutdown Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Another PCNS/Shutdown Question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
kudrow_apc
Crewman kudrow_apc
Crewman

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
1
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Another PCNS/Shutdown Question

Hi all,

I am referring to this post (http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/5701/ups-nm... however before I try this I would like to clarify first.

I have a single server running PCNS connected to a AP9630. I want the server to stay online for as long as possible and only shut down once the UPS has reached it's low battery setting (15 minutes). I want the UPS to power back on after a power outage and reboot the server.

What configuration is needed in both sides? I cannot seem to find a setting in PCNS to sort of "take instruction from the UPS", only timers and whatnot that will schedule a shutdown possibly prematurely if hte UPS still has available run time.

Also, what are the other settings in the AP9630, including "Duration of shutdown" and "End of shutdown".

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Hi,

PCNS will start a shutdown automatically when the UPS reaches the low battery setting configured in the NMC. By default, PowerChute will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.

On 11/8/2015 3:45 AM, Brady said:

Also, what are the other settings in the AP9630, including "Duration of shutdown" and "End of shutdown".

This information can be found by clicking on NMC help:

Duration of Shutdown
Sleep Time Defines how long the UPS sleeps (keeps its output power turned off) when you use the "Control" menu "Put UPS To Sleep" option.
End of Shutdown
Minimum Battery Capacity The minimum battery capacity, as a percentage of full capacity, required in order for the UPS to end its sleep time (or turn back on when rebooted) and resume providing output power.
Return Delay Defines how long the UPS waits before it turns on after a shutdown that was caused by a power failure, after a scheduled shutdown, or after a shutdown initiated by a Control command. If the battery is depleted below the percentage configured as "Minimum Battery Capacity", the UPS first waits until the battery is recharged to that minimum capacity. If the battery is depleted below the capacity to provide the runtime configured as "Return Runtime Duration", the UPS first waits until the battery is recharged to the capacity that is able to provide that runtime.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Hi,

PCNS will start a shutdown automatically when the UPS reaches the low battery setting configured in the NMC. By default, PowerChute will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. Shutdown cannot be disabled for these events using the PowerChute user interface.

On 11/8/2015 3:45 AM, Brady said:

Also, what are the other settings in the AP9630, including "Duration of shutdown" and "End of shutdown".

This information can be found by clicking on NMC help:

Duration of Shutdown
Sleep Time Defines how long the UPS sleeps (keeps its output power turned off) when you use the "Control" menu "Put UPS To Sleep" option.
End of Shutdown
Minimum Battery Capacity The minimum battery capacity, as a percentage of full capacity, required in order for the UPS to end its sleep time (or turn back on when rebooted) and resume providing output power.
Return Delay Defines how long the UPS waits before it turns on after a shutdown that was caused by a power failure, after a scheduled shutdown, or after a shutdown initiated by a Control command. If the battery is depleted below the percentage configured as "Minimum Battery Capacity", the UPS first waits until the battery is recharged to that minimum capacity. If the battery is depleted below the capacity to provide the runtime configured as "Return Runtime Duration", the UPS first waits until the battery is recharged to the capacity that is able to provide that runtime.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of