Allowable interrupting capacity of rack PDU (AP8888)

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
karbonphiber_apc
Lieutenant JG
Lieutenant JG
0 Likes
3
198

Allowable interrupting capacity of rack PDU (AP8888)

This was originally posted on APC forums on 12/8/2013


Links are down on APC's website *cough* as usual *cough* and i can't access the specifications for the AP8888 rack PDU. Anyone know what the allowable interrupting capacity of the AP8888 metered rack PDU is? 10KAIC? 22KAIC?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
199

Re: Allowable interrupting capacity of rack PDU (AP8888)

This reply was originally posted by Angela on APC forums on 12/10/2013


As I know we are already discussing this offline at the same time, I'd like to end the forum discussion and just continue with the other conversion we have going since I was just duplicating what you asked our product manager.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
199

Re: Allowable interrupting capacity of rack PDU (AP8888)

This reply was originally posted by Angela on APC forums on 12/9/2013


We currently do not have a kAIC rating for our Rack PDUs. We do know that the rating is less than 10 kAIC.

karbonphiber_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
199

Re: Allowable interrupting capacity of rack PDU (AP8888)

This was originally posted on APC forums on 12/10/2013


seeing as how the AP8888 is a 240-415Vac, 3ph RPDU, and the distribution scheme eliminates the need for an output isolation transformer on a PX500 configured for 415Vac output, what would happen to the PDU if exposed to a short circuit of 18kA? Would it blow up?

BillP
Administrator Administrator
Administrator
0 Likes
0
200

Re: Allowable interrupting capacity of rack PDU (AP8888)

This reply was originally posted by Angela on APC forums on 12/10/2013


As I know we are already discussing this offline at the same time, I'd like to end the forum discussion and just continue with the other conversion we have going since I was just duplicating what you asked our product manager.