After installing new batteries, my UPS 5000 sends alerts "UPS: The battery power is too low..."

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Benci_apc
Cadet
0 Likes
1
214

After installing new batteries, my UPS 5000 sends alerts "UPS: The battery power is too low..."

This was originally posted on APC forums on 6/18/2015


Hi

I installed new batteries on 2 UPS 5000. They both have an alert "UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.". I did turn off and on 1 of them, but ne change.

First UPS

Model: SU5000R5TBx120,  Firmware Revision: 112.14.M, 

Network Management Card: AP9617, Hardware Rev. A10; sumx version: v3.7.2; aos version: v3.7.3

UPS status:

Battery Capacity: 100%

Battery Voltage: 55.65 VDC

Load: 40.5%

It fires 2 alerts every minute: "UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately."

What should I do?

Thanks you

Ben C

Second UPS 

Model: SU5000RMT5U, Firmware rev. 112.14.M; AP9606

UPS status: Discharged

Battery capacity: 100%, Battery voltage: 54.55 VDC, Load power: 43.6% WATS;  Runtime remaining: 0 minutes


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
215

Re: After installing new batteries, my UPS 5000 sends alerts "UPS: The battery power is too low..."

This reply was originally posted by Angela on APC forums on 6/18/2015


The UPS probably needs to update its runtime.

You'll want to read through this article first (http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538). You probably have the flashing battery bar graph mentioned in the title. I'd try issuing a runtime calibration command through the management card. If it does not work or rejects it, then we'd try the manual calibration mentioned. If that doesn't work, we will calibration keys available that will fix this issue through your serial port for you. If I can't get one of those sent to you, then we could maybe provide you with some special instructions if you have the APC 940-0024 or 940-1524 serial cable available with a computer.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
216

Re: After installing new batteries, my UPS 5000 sends alerts "UPS: The battery power is too low..."

This reply was originally posted by Angela on APC forums on 6/18/2015


The UPS probably needs to update its runtime.

You'll want to read through this article first (http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538). You probably have the flashing battery bar graph mentioned in the title. I'd try issuing a runtime calibration command through the management card. If it does not work or rejects it, then we'd try the manual calibration mentioned. If that doesn't work, we will calibration keys available that will fix this issue through your serial port for you. If I can't get one of those sent to you, then we could maybe provide you with some special instructions if you have the APC 940-0024 or 940-1524 serial cable available with a computer.