Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

APC UPS 3000 RM - Battery Module wont come out

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: APC UPS 3000 RM - Battery Module wont come out
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
rmillersbs_apc
Crewman rmillersbs_apc
Crewman

Posted: ‎2021-06-29 11:42 PM

0 Likes
6
1857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

APC UPS 3000 RM - Battery Module wont come out

This was originally posted on APC forums on 2/23/2013


Anyone have any problems with removing the battery module for an APC 3000RM series UPS. I removed the three screws, but the module can only be shimmied left/right and up/down a bit. Anyone experience this before? Cant imagine what's locking it up. I even removed the top case cover and I'm stuck.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • apc
  • battery
  • can't
  • module
  • remove
  • replacement
  • rm
  • stuck
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
trip777_apc
Crewman trip777_apc
Crewman

Posted: ‎2021-06-29 11:42 PM

0 Likes
1
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This was originally posted on APC forums on 4/29/2015


Thanks for the advice. The flat blade screwdriver worked well getting the two batteries out of the frame. Swapped connectors, reinstalled, and back in business.

See Answer In Context

Reply
Share
Replies 6
Battman_apc
Commander Battman_apc
Commander

Posted: ‎2021-06-29 11:42 PM

0 Likes
0
1858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This was originally posted on APC forums on 2/28/2013


I've dealt with this situation numerous times. The first thing to try is unplug the battery string completely and try using a large straight blade screwdriver to pry on the battery casing from the left and right sides - lever the screwdriver against the metal ups chassis casing to the left and right of the battery opening alternately to wiggle it out. If the screwdriver tip is sharp enough it will bite into the plastic of the battery and get extra grip. Don't worry if you crack the case of the battery it will not cause a problem (re leaks or shorts) as the batteries are toast anyway. If that doesn't work your only choice is to unplug the battery, power down the ups, remove it from the rack, let the UPS sit for a couple of days to drain any charge on the capacitors and then take the top off the UPS and get the batteries out one by one possibly removing some interior screws to losen the battery compartment walls. Some are riveted though!

Good luck,

Dave

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:42 PM

0 Likes
0
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This reply was originally posted by Joe on APC forums on 2/24/2013


Sounds like the battery has become "swollen" for any of a variety of issues including an extended overcharge condition, etc. It's going to take sheer physical force to pry the battery out.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:42 PM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This reply was originally posted by Angela on APC forums on 2/25/2013


what i would suggest if you haven't done it already is allow the battery to cool off and make sure it is not continuing to charge. you should power down the UPS completely (which means your attached load too needs to be off) and then disconnect the battery. a fan also might be helpful on the battery to cool it down and maybe shrink it a bit enough to wiggle it out of there.

before i say all that actually - is the battery even warm? how old is it?

Reply
Share
rmillersbs_apc
Crewman rmillersbs_apc
Crewman

Posted: ‎2021-06-29 11:42 PM

0 Likes
0
1861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This was originally posted on APC forums on 2/25/2013


Thanks guys for the ideas thus far. The battery is quite old (3 years). I have not disconnected it for more than 15 minutes at a time, since doing so leads to it chirping every few seconds, which is annoying. Is there a way to turn this off, or to disable the 1 minute chirping every 5 hour cycle until I get this resolved?

It doesn't feel swollen so much as though something is blocking it. As I mentioned, I can shimmy it an eighth of an inch left/right and up/down at the front, but it has only about an eighth of an inch pull before it locks, and I've pulled the thing pretty dang hard. I'm thinking of shutting down the servers its powering and pulling it out of the rack, but that's a lot of inconvienience, headache and work that I'm trying to avoid.

Classic case of a 10 minute job turning into something else entirely 😞

Reply
Share
trip777_apc
Crewman trip777_apc
Crewman

Posted: ‎2021-06-29 11:42 PM

0 Likes
1
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 11:42 PM

This was originally posted on APC forums on 4/29/2015


Thanks for the advice. The flat blade screwdriver worked well getting the two batteries out of the frame. Swapped connectors, reinstalled, and back in business.

Reply
Share
SteveSJ
SteveSJ
Cadet

Posted: ‎2022-04-20 09:18 AM

In response to trip777_apc
0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-04-20 09:18 AM

I can confirm that the flat blade screwdriver works.  I started out side to side but also used it on the bottom.  Takes A LOT of patience.  If it doesn't work at first, take a break and come back to it later.

  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc