Hi, this UPS is showing no earth on a fluke mains tester SM100 when on battery power, is this correct? On mains supply in, it is normal showing correct earth bond.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:28 AM . Last Modified: 2024-03-18 04:38 AM
Hi,
You will have ground but will not have neutral. When the UPS switches to battery hot and neutral are broken to prevent back feed. We have Kbase FA156549 that discusses this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:28 AM . Last Modified: 2024-03-18 04:38 AM
Hi,
You will have ground but will not have neutral. When the UPS switches to battery hot and neutral are broken to prevent back feed. We have Kbase FA156549 that discusses this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of