Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84522members
353759posts

APC PowerChute UPS redundancy (via NMC)

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
xd90europe_apc
Cadet
0 Likes
2
160

APC PowerChute UPS redundancy (via NMC)

This was originally posted on APC forums on 4/5/2013


     Hello everybody!

     I have to install APC PowerChute on all servers. I have one APC UPS-SURT8000XLI mounted for each racks connected through NMC to my network (LAN). I wish to have redundancy between the UPS. I described my problems in the following pictures:

1083_8.png

1082_apc.png


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
160

Re: APC PowerChute UPS redundancy (via NMC)

This reply was originally posted by Bill on APC forums on 4/5/2013


Hi,

We have application note #98 http://www.apcmedia.com/salestools/BKIR-6R9NX5/BKIR-6R9NX5_R2_EN.pdf

that should answer your questions. As for shutting the domain controller down last, that can be done by either setting either the on battery event or by allowing the system to wait for low battery. Example: configure none essential server to shutdown when UPS have been on battery for 10 minutes and the domain controller to shutdown when UPS have been on battery for 20 minutes.

You should also read the PCNS help file section on redundant UPS configuration and critical events.

Hope this information help.  

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
161

Re: APC PowerChute UPS redundancy (via NMC)

This reply was originally posted by Bill on APC forums on 4/5/2013


Hi,

We have application note #98 http://www.apcmedia.com/salestools/BKIR-6R9NX5/BKIR-6R9NX5_R2_EN.pdf

that should answer your questions. As for shutting the domain controller down last, that can be done by either setting either the on battery event or by allowing the system to wait for low battery. Example: configure none essential server to shutdown when UPS have been on battery for 10 minutes and the domain controller to shutdown when UPS have been on battery for 20 minutes.

You should also read the PCNS help file section on redundant UPS configuration and critical events.

Hope this information help.  