Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

APC NMC AP9617

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: APC NMC AP9617
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
lupeatx_apc
Crewman lupeatx_apc
Crewman

Posted: ‎2021-06-29 04:57 AM

0 Likes
8
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

APC NMC AP9617

This was originally posted on APC forums on 11/28/2012


I am in need of some help with setting this up. I downloaded the Device IP configuration utility but it does not detect any of the cards. I already tried the ARP method but still nothing. We can seem to find the serial cables to try it that way. Any other way to get this done?

Is there a reason why the utility can't locate the unconfigured cards? Can the cards be reset to factory settings? These cards have always been on the UPS's but no one ever set them up.

The other thing I did was replaced the AP9617 with a brand new, out fo the box AP 9630 and the utility can't seem to find it. What gives?

Anything helps.

Thanks!

Message was edited by: lupeatx

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • NMC
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This reply was originally posted by Angela on APC forums on 12/3/2012


yes, as long as it does not get a DHCP address from your network before you run the utility to search for unconfigured cards. if it does get a DHCP address, the status LED will change to solid green on that card as well. otherwise, you can use the utility to search for configured cards and search an IP range - for instance, if you know the DHCP scope/pool, you can search for a range of addresses.

if the wizard does not work, the only other thing could be a blocked port which prevents it from searching for the cards. i believe it uses SNMPv1 to query the card after it finds it too to display a few things like the firmware version in the table that returns results.

See Answer In Context

Reply
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This reply was originally posted by Angela on APC forums on 12/4/2012


the official procedure is to turn the UPS off and braindead it. i never do it and there is a very slim chance anything would happen. i've done it hundreds of times so my expert advice is just to hot-swap them.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This reply was originally posted by Angela on APC forums on 11/28/2012


the first thing i would do is verify the lights on these cards. if you look at the network jack, the link LED is on the left and the status LED is on the right. can you tell me the color of the lights and if they are solid or flashing?

AP9630 defaults to DHCP so if the card gets a DHCP address, the device IP wizard will not discover it unless you specify to search for a specific DHCP pool range. by default the wizard searches for unconfigured cards on the network.

AP9617 comes for DHCP with option 43 vendor cookie required by default.

Reply
lupeatx_apc
Crewman lupeatx_apc
Crewman

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This was originally posted on APC forums on 11/28/2012


link LED is flashing orange and the status LED is solid green.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This reply was originally posted by Angela on APC forums on 11/28/2012


ok, that status LED being solid green means it has valid IP settings (well in the valid format, not maybe the right IP for your network). so unless you know the IP range to search, the device IP wizard will not find it. ARP won't work when a card is configured either.

there is no way to reset AP9617 without logging into it. can you try and track down the serial cable again? for AP9617, you'll need to look for 940-0024/940-1524..its a black cable with the part # engraved on the connector.

Reply
lupeatx_apc
Crewman lupeatx_apc
Crewman

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This was originally posted on APC forums on 12/3/2012


So I can't find the serial cable for this. I did find an AP 9630 (new) and I saw that I can replace the ap9617 with. Since it's brand new I will be able to find it using the Device IP Config Utility right?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This reply was originally posted by Angela on APC forums on 12/3/2012


yes, as long as it does not get a DHCP address from your network before you run the utility to search for unconfigured cards. if it does get a DHCP address, the status LED will change to solid green on that card as well. otherwise, you can use the utility to search for configured cards and search an IP range - for instance, if you know the DHCP scope/pool, you can search for a range of addresses.

if the wizard does not work, the only other thing could be a blocked port which prevents it from searching for the cards. i believe it uses SNMPv1 to query the card after it finds it too to display a few things like the firmware version in the table that returns results.

Reply
lupeatx_apc
Crewman lupeatx_apc
Crewman

Posted: ‎2021-06-29 04:57 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:57 AM

This was originally posted on APC forums on 12/3/2012


I am in. Going thru and configuring everything now. Still will need to configure the other ap9617 somehow.

One more question. I have 2 other UPS without NMC, now can I install the NMC WITHOUT turning off the UPS?

Reply
lupeatx_apc
Crewman lupeatx_apc
Crewman

Posted: ‎2021-06-29 04:58 AM

0 Likes
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:58 AM

This was originally posted on APC forums on 11/30/2012


I tried two ranges but nothing is coming up. I will look for the serial cable. Let's hope I find one.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc