APC NMC 9617 compatibility question

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
DThimsen_apc
Crewman
Crewman
0 Likes
3
160

APC NMC 9617 compatibility question

This was originally posted on APC forums on 4/16/2015


We've been running on older APC Smart-UPS devices for years and had one recently fail.  I ordered and received a new APC Smart-UPS SMT2200, and noticed that the SmartSlot has changed slightly and now has tabs that pass throught the NMC faceplate.  Are the APC 9617 cards we have incompatible with the newer SmartUPS systems?

Thanks,

Don


Accepted Solutions
DThimsen_apc
Crewman
Crewman
0 Likes
0
160

Re: APC NMC 9617 compatibility question

This was originally posted on APC forums on 4/17/2015


Angela/voidstar,

Thanks for the info...  I've now ordered a coupld of AP9630s.

Thanks,

Don

See Answer In Context

3 Replies 3
voidstar_apc
Janeway
Janeway
0 Likes
0
160

Re: APC NMC 9617 compatibility question

This was originally posted on APC forums on 4/17/2015


Yes, newer UPS models such as the SMT2200 are incompatible with the AP9617 card. The AP9630 is the direct replacement. While the AP9630 will also work on older UPSes, offers additional features, and are much faster processing HTTPS and SSH connections, I would stick with using the existing AP9617 cards on them for now.

BillP
Administrator Administrator
Administrator
0 Likes
0
160

Re: APC NMC 9617 compatibility question

This reply was originally posted by Angela on APC forums on 4/17/2015


Here is a link to a relatively new UPS Network Management Card compatibility chart -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA237786 

DThimsen_apc
Crewman
Crewman
0 Likes
0
161

Re: APC NMC 9617 compatibility question

This was originally posted on APC forums on 4/17/2015


Angela/voidstar,

Thanks for the info...  I've now ordered a coupld of AP9630s.

Thanks,

Don