AP9641 intermittently loses connection to cisco catalyst 9300 switch

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9641 intermittently loses connection to cisco catalyst 9300 switch
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
jackson3
jackson3
Cadet

Posted: ‎2022-11-22 07:55 AM

0 Likes
4
2250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-22 07:55 AM

AP9641 intermittently loses connection to cisco catalyst 9300 switch

I have several sites with new APC SMT3000 UPS's that constantly lose connection to the network. The network card firmware is 2.2.1.1. This is constantly causing the monitoring system to send out emails and warnings. Dialing into the card there is nothing in the logs to show the card went down.

 

At the site, I could see the link light on the front of the switch go off, yet the link light on the card never did, so i am wondering if the switch is having an issue where it constantly has to re-establish a connection. I do not have this problem with the AP9361, I swapped my last on out with one of the troublesome UPS's and all problems went away.

 

I have replaced the card with another AP9641, moved to a different port on the switch, used 2 different brand new LAN cables, changed the port speed on the card from automatic to 100 and 10 full duplex, reset the switch ports to default, tried turning on and off POE, still having the same problem.

 

I have two SMT1500 UPS's on the network not having any issues with the AP9641, same set up except the firmware on the cards is 1.3.3.1. They are not experiencing any problems. All UPS's have the same ID18 9.8 firmware in them.

 

One final thing, if I start a continuous ping from my laptop to the network card, it never loses connection, even over several hours, yet as soon as i stop the ping the intermittent communication loss starts.

 

Any suggestions?

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-22 06:44 PM

0 Likes
0
2240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-22 06:44 PM

Hi @jackson3 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  I am sorry to hear about the issue that you are experiencing with the AP9641.

 

If you go to About > Network and check the Uptime, this is one way for you to confirm if it really loses communication.  We recommend applying the latest NMC3 firmware to resolve the problem.

 

Please download and apply the firmware v2.3.1.1 below to the NMC3s that you have.

 

SFNMC3SU231 - UPS Network Management Card 3 Firmware v2.3.1 for Smart-UPS with AP9640/41/43 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

theotang-bm
theotang-bm
Cadet

Posted: ‎2024-08-08 07:11 AM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-08 07:11 AM

I have this same problem.  AP9641 application module v2.0.0.5, apc os (aos) v2.0.0.6, and apc boot monitor v1.4.0.2.  Will try the new firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: ‎2024-08-09 08:43 PM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-09 08:43 PM

The switch port should be set to auto auto and the card set to auto for speed and duplex. Also leave the POE turned off on that port. 

Also if when you say “monitoring system”I am assuming you have something besides internal card email set up and probably using SNMPv1 or V3. If that is true make sure that only one version (either 1 or 3) is enabled. if both are on this can/will cause false alerts as well

Reply

Link copied. Please paste this link to share this article on your social media post.

mwitt
Crewman mwitt
Crewman

Posted: ‎2024-10-22 02:42 PM

0 Likes
0
640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 02:42 PM

Hi @jackson3, 

 

did you find a resolution to your issue? I am facing the similar issue. It connected when i ping but when its left for 2 min it drops connection.

 

I have NTP update set at one hour as a test, so every hour i at least get access to it remotely. Another identical one is set longer (24 hours) and doesn't reconnect often

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of