Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP9630 no LEDs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP9630 no LEDs
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
chrisbbb_apc
Ensign chrisbbb_apc
Ensign

Posted: ‎2021-06-29 04:50 AM

0 Likes
4
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

AP9630 no LEDs

This was originally posted on APC forums on 8/12/2016


We have a new AP9630 in a new SMX2200HV4U UPS. There are no LEDs lit on the AP9630. It has the APC serial cable connected, & a 100M LAN cable is connected (this LAN connection works when plugged instead into a computer). Ive held the reset button down for 20+secs and no flashing LED. Card says 640-1110A-Z_REV05, made 2008. Help! praying the NMC is good. 

Thanks, Chris

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9630
  • dead
  • leds
  • no
  • reset
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:50 AM

0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

This reply was originally posted by Tommy on APC forums on 8/16/2016


Hi Chris,

I agree, that doesn't look good for the AP9630. To clarify, you put that card into the older SmartUPS 2200XL correct? If you haven't, you can hotswap that card and there will be no issues for either the load/equipment or the UPS (see this link). If that's the case, I would assume the card needs to be replaced. I see your location says Fiji, and unfortunately, I'm not aware of their warranty/return policy but that card you have was manufactured in 2010 based on the serial number. Here in the US/Canada, it's 2 years from purchase date from an authorized reseller (not manufacture date). 

Let me know if you need anything else, and I apologize for the issues you are having.

- Tommy

See Answer In Context

Reply
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:50 AM

0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

This reply was originally posted by Tommy on APC forums on 8/15/2016


Hi Chris,

Do you have any other UPS's on site? If so, I would try to swap this card into another UPS to see if the issue lies with the smartslot (slot where the AP9630 slides into) on the UPS or the card itself. Conversely, if you have other AP9630's/AP9631's/AP9635's, you can try swapping those into this UPS with the same goal (either the card or the smartslot). If you find that other cards don't work in this UPS (meaning it makes more sense to be a smartslot issue), I would suggest brain deading the UPS (see this link). 

If you can't isolate it at all, let's get some more info on your setup to see if anything else makes sense.

- Is this a new install or was previously working (I assume new install since you said it was new but figured I would clarify)? If so, any circumstances change?

- What's the serial number off the NMC?

- Is there any notable physical damage on the card? (capacitor fell off, etc.) You can post a picture of the card, and I'll compare against ones I have.

- Is the reset button still present? I've seen issues where someone in the past has broken it trying to reset the card. 

- To clarify, you don't see any LED's blink at any time right?

Thanks,

Tommy

Reply
chrisbbb_apc
Ensign chrisbbb_apc
Ensign

Posted: ‎2021-06-29 04:50 AM

0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

This was originally posted on APC forums on 8/15/2016


Tommy, hi, excellent to hear from you

- New install, ie first use of this new UPS & this new NMC 2.

- have not once seen any light from the Status & Link LEDs on this card

- 2 photos of the card, attached

- I have "brain-deaded" (not a word) the UPS, I do it when i replace the card, by 1. output off  2. unplug input  3. open front & pull connector off battery.   (we have just one NMC)

- UPS Manual shows that the last item in the Menu (advanced) - About -.. is the details of the NMC. Our last menu item is the one before, zero mention of the NMC.

- btw  card says "(Copyright symbol) 2008" not "made 2008"

- UPS has USB cable to a test Windows server, I'ved uninstalled the newly-installed PowerChute software after reading that Powerchute & the NMC would not be used together.

- serial cable to server: Putty serial no access ie no screen response to a prompt

- cleaned card edge connectors with CRC Contact Cleaner.

- numbers (bottom) Bangalore  AP9630  barcode ZA1052008995, (top) barcode 4626819900037907

- caps are secure. no sign of physical damage, incl under a magnifier

- reset button has distinctive muted soft momentary click feel when activated

- we have a production Smart-UPS2200XL, would have to arrange a big outage or hot-swop card. I was reading Forum responders are OK with hot-swop (cant find those post again in this moment), card has the two longer power edge connectors, are we OK? otherwise, we wait for an outage. That UPS is old & being replaced, it once had an NMC card that was presumed to have failed & was binned, maybe its smart-slot is nogo? Anyway, if ours does work in that, that's big news.

Thanks !

Chris

Attachments
Reply
chrisbbb_apc
Ensign chrisbbb_apc
Ensign

Posted: ‎2021-06-29 04:50 AM

0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

This was originally posted on APC forums on 8/16/2016


Did the outage, made the older UPS braindead, installed card and power all UP. No LEDs on card. Insert LAN cable, same. Reset, same.

Doesnt prove anything as we dont know if that smartslot is good or not.

btw, have the paper record of tests performed on the new UPS at build May 2016; both tests for smartslot show Pass. Doesnt mean slot is good now. otoh, doesnt look good for the NMC2.

Thoughts?

Thanks

Chris

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:50 AM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:50 AM

This reply was originally posted by Tommy on APC forums on 8/16/2016


Hi Chris,

I agree, that doesn't look good for the AP9630. To clarify, you put that card into the older SmartUPS 2200XL correct? If you haven't, you can hotswap that card and there will be no issues for either the load/equipment or the UPS (see this link). If that's the case, I would assume the card needs to be replaced. I see your location says Fiji, and unfortunately, I'm not aware of their warranty/return policy but that card you have was manufactured in 2010 based on the serial number. Here in the US/Canada, it's 2 years from purchase date from an authorized reseller (not manufacture date). 

Let me know if you need anything else, and I apologize for the issues you are having.

- Tommy

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc