Hi,
We purchased "SMX3000RMLV2U" and "AP9620" Legacy Communications Card.
- We physically installed the AP9620 in to the Smart Slot of the SMX3000.
- We connected the battery cable of SMX3000
- We turned on the SMX3000 UPS.
- We haven't done any firmware update.
Problem:
STATUS LED of the AP9620 first flashing green as expected, then turns to flashing RED.
Do I need to perform some kind of software configuration or firmware update on SMX3000 UPS in order to work with AP9620? According to LCC Compatibility Matrix (below), Compatibility is fully supported on SMX3000.
I really appreciate any help.
| LCC Compatibility Matrix | |
| Supported UPS Models | Compatibility Notes | 
| SMT750 SMT1000 SMT1500 SMT2200 SMT3000 | Requires ""COM 02.1"" Firmware or later | 
| SMT750I SMT1000I SMT1500I SMT2200I SMT3000I | Compatibility is fully supported | 
| SMT750RM SMT1000RM SMT1500RM SMT2200RM SMT3000RM | Compatibility is fully supported | 
| SMX750 SMX1000 SMX1500 | Requires Firmware ""UPS 03.1 / COM 03.0"" or later | 
| SMX750I SMX1000I SMX1500I | Compatibility is fully supported | 
| SMX2000 SMX2200 SMX3000 | Compatibility is fully supported | 
| SURTD3000 SURTD5000 | Requires UPS Firmware 5.1 or later | 
Regards
Baris Sukay
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Hi Angela,
I tried once more and it worked. I dont know what i did wrong before may be timing was not fast enough but now i can see the solid green LED.
Thanks a lot for your help
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
FIRMWARE INFORMATION
Firmware Revisions written on the SMX3000 screen:
UPS FIRMWARE 1: UPS 07.4
UPS FIRMWARE 2: MCU 07.4
UPS FIRMWARE 3: UBL 07.4
UPS FIRMWARE 4: MBL 06.0
AP9620 Firmware Revision: LCC001.6 / LCB 05.5
Thanks in advance for helping
Baris
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Yes, it should work according to what I can find and of course per what the knowledge base says.
I suggest you contact your local support office via email or phone to obtain the upgrade file and procedure for LCC v2.2 to see if that resolves the issue. If you have trouble with that, let me know. It is possible a newer UPS firmware update has broken compatibility or communication with the LCC but I don't see that specifically listed as an issue anywhere and SMX3000 SKUs have been supported by LCC from the get go as documented.
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Hi Angela, thanks for your reply,
I contacted APC. They sent me a file named "LCC_02.2.enc" with an instruction pdf contains firmware update procedure (LCC Firmware Update Instructions.pdf). I followed the procedure, unfortunately it didn't work. In fact, it looks worse now. Before the upgrade attempt, when i insert the LCC, the status led was flashing green after a minute it was turning to flashing red, after unsuccessful upgrade attempt, the status LED is always flashing red.
I' ve tried the procedure with hyper terminal and minicom (linux) on different laptops with the same result. Now, i can read messages from LCC ony if i connect with 19.200 baud. It stuck there. When I connect with 2.400 baud, strange symbols appear. Wheb I connect with 19.200 baud, i see CCCC characters.
I am stuck Angela any suggestions?
Thanks for helping.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
When you see CCCC, it means the LCC is waiting for the file transfer and you need to send the file through your terminal program like hyperterminal or something else that supports XMODEM serial protocol. CCCC is good at least though.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
You're sure you're specifying XMODEM and not ZMODEM or YMODEM protocol when you browse and send the LCC v2.2 .enc file? You need to make sure the file is being sent as soon as you see CC's and not wait until it gets towards the end where it may timeout before the transfer begins.
What you're seeing seems normal for steps 10, 11, and 12 in the PDF except for the fact that it seems v1.6 has been somehow erased from the card since it says no application in memory..
If you can validate what I ask, I'll need to check on this further.
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:12 AM . Last Modified: 2024-02-29 11:29 PM
Hi Angela,
I tried once more and it worked. I dont know what i did wrong before may be timing was not fast enough but now i can see the solid green LED.
Thanks a lot for your help