AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Rooster_apc
Ensign
Ensign
0 Likes
4
427

AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This was originally posted on APC forums on 2/23/2016


I recently suffered a destroyed AP7723 ATS and UPS (SURT2000) during commissioning/testing. The defect occurred having just added the ATS to an existing UPS system whilst manually switching between 2 x UPS input supplies (2 x SURT2000) whilst on load (approx 1100W). The UPS generated an 'over-voltage' error and is now stuck in permanent bypass mode. Trouble is, I don't know if the ATS destroyed the UPS or the other way-round. 

Having replaced both the UPS and APS, I then attached an earth bond to the chassis of the ATS. I then continually repeated the ATS input selection testing and the install worked seamlessly as designed.

I have no idea if I was just unlucky with the first failure, or if the addition of an earth bond made any difference in terms of voltage suppression during switch-over. 

I assume the previous earth path was only via the 2 x UPS inputs, so I have no idea how these are referenced to each other - or to chassis ground. The brief ATS instructions refer to fitting an earth bond if fault current is unknown (or greater than a certain figure) but could the lack of earth-bond have contributed to the original failure?


Accepted Solutions
Rooster_apc
Ensign
Ensign
0 Likes
0
427

Re: AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This was originally posted on APC forums on 3/7/2016


Hi Bill,

I've checked the faulty ATS again and can confirm that the Source A 24V PSU is dead i.e. reading 0V via serial or Ethernet with an input supply present. You can hear a relay 'click' when the lead is inserted into Source A, but you have to power the unit up via Source B.

I've attached a text version of the log file, which shows many 'over frequency violation Source A' errors. In this case, both sources were from SURT2K UPS' - albeit the one feeding Source A failed simultaneously to the ATS input failure.

See Answer In Context

Attachments
4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
427

Re: AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This reply was originally posted by Bill on APC forums on 2/25/2016


Hi,

The ATS would be using the ground of the source (the UPS in the first case) - did you do any configuration to the ATS before deploying it? Is it possible to send us the configuration files/event logs/event counts of the ATS?

Rooster_apc
Ensign
Ensign
0 Likes
0
427

Re: AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This was originally posted on APC forums on 3/3/2016


Hi Bill. The only thing I did prior to fitment was upgrade the firmware to 3.9.0, select 'no source preference' and lock-out the front panel button. No other parameters were changed.

BillP
Administrator Administrator
Administrator
0 Likes
0
427

Re: AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This reply was originally posted by Bill on APC forums on 3/7/2016


Hi,

Without the logs it is difficult to say what may have caused the issue. As mentioned earlier the ATS should have been grounded while plugged into a UPS assuming the UPS was grounded. 

Rooster_apc
Ensign
Ensign
0 Likes
0
428

Re: AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

This was originally posted on APC forums on 3/7/2016


Hi Bill,

I've checked the faulty ATS again and can confirm that the Source A 24V PSU is dead i.e. reading 0V via serial or Ethernet with an input supply present. You can hear a relay 'click' when the lead is inserted into Source A, but you have to power the unit up via Source B.

I've attached a text version of the log file, which shows many 'over frequency violation Source A' errors. In this case, both sources were from SURT2K UPS' - albeit the one feeding Source A failed simultaneously to the ATS input failure.

Attachments