Posted: 2022-01-27 05:51 AM
Hi,
We had a power surge a few days ago and now I cannot clear this issue on the AP4423.
Source A is mains UK power and Source B is UPS power.
I have removed the unit from the cab and plugged in else where but have the same issue, I cant see any external fuses that can be replaced.
Help!!
Thanks in advance.
Posted: 2022-01-31 03:20 AM
Added an image from the unit, Source B is disconnected as it's been removed from the cabinet until this can be resolved
Posted: 2022-02-02 06:15 AM
Hi
Just to be clear, you tried moving the ATS to different power sources, but the issue remained, with source B being unavailable?
If so, I am curious as to what version of the firmware you are running on the unit, and would you be able to share the support file from the unit?
-> https://www.apc.com/ie/en/faqs/FA156131/
The process described for NMC2 is applicable for this unit.
Best regards
Tonny
Posted: 2022-02-03 02:39 AM
Hi,
Yes, I moved the APC from the CAB and plugged it in somewhere else in the building, I believe the server room is on its own circuit so I was hoping it would either clear the issue or give me an idea of the issue.
Serial Number
5A1838T68992
Firmware Version
4.1.9
Firmware Date
03/16/17
Downloader Version
4.3
Due to the issue, the APC has been taken out of the live cab as its not working anyway, but i have kept it plugged in to try and resolve it.
Posted: 2022-02-03 04:28 AM
Hi
I think the next step should be to upgrade to latest firmware version for the unit, to ensure that is is not a software based issue.
You can find the firmware here -> https://www.se.com/ww/en/download/document/APC_ATS4G_704_EN/
After the reboot, I suggest doing a power-cycle of the unit.
If that does not help, you are most likely looking at a issue with the hardware, and in that case you should contact your local CCC in regards to a possible replacement under the warranty.
Best regards
Tonny
Posted: 2022-02-03 05:08 AM
Doesnt seem to have worked. Although I haven't been able to power cycle due to not being on-site.
Posted: 2022-02-03 05:31 AM
Hi
I think you might be looking at the wrong firmware there.
The firmware you are upgrading is the firmware for the Network management module in the unit.
If you navigate to [About] -> [Network] on the web interface, you can find the information under application module.
The version number presented there is the one you should be looking at.
Best regards
Tonny
Posted: 2022-02-03 05:35 AM
I see, its now v7.0.4 but the error is still present.
Posted: 2022-02-03 05:53 AM
Hi
In that case you are likely looking at a hardware issue.
I would suggest opening a case with your local CCC and get them involved, especially if the unit is under warranty.
Best regards
Tonny