Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82522members
350124posts

AP4423 Possible open fuse Source A

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Spardha
Crewman
Crewman
0 Likes
8
667

AP4423 Possible open fuse Source A

Hi,

 

We had a power surge a few days ago and now I cannot clear this issue on the AP4423.  

 

Source A is mains UK power and Source B is UPS power.

 

I have removed the unit from the cab and plugged in else where but have the same issue, I cant see any external fuses that can be replaced.

 

Help!!

 

Thanks in advance.

Tags (1)
8 Replies 8
Spardha
Crewman
Crewman
0 Likes
7
653

Re: AP4423 Possible open fuse Source A

Added an image from the unit, Source B is disconnected as it's been removed from the cabinet until this can be resolved

apc4423 error.JPG

Tags (1)
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
6
642

Re: AP4423 Possible open fuse Source A

Hi

 

Just to be clear, you tried moving the ATS to different power sources, but the issue remained, with source B being unavailable?

If so, I am curious as to what version of the firmware you are running on the unit, and would you be able to share the support file from the unit?

-> https://www.apc.com/ie/en/faqs/FA156131/

The process described for NMC2 is applicable for this unit.

 

Best regards

Tonny

Tags (1)
Spardha
Crewman
Crewman
0 Likes
5
635

Re: AP4423 Possible open fuse Source A

Hi,

 

Yes, I moved the APC from the CAB and plugged it in somewhere else in the building, I believe the server room is on its own circuit so I was hoping it would either clear the issue or give me an idea of the issue.

 

Serial Number
5A1838T68992

Firmware Version
4.1.9
Firmware Date
03/16/17
Downloader Version
4.3


Due to the issue, the APC has been taken out of the live cab as its not working anyway, but i have kept it plugged in to try and resolve it.

Attachments
Tags (1)
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
4
631

Re: AP4423 Possible open fuse Source A

Hi

 

I think the next step should be to upgrade to latest firmware version for the unit, to ensure that is is not a software based issue.

You can find the firmware here -> https://www.se.com/ww/en/download/document/APC_ATS4G_704_EN/

 

After the reboot, I suggest doing a power-cycle of the unit.

 

If that does not help, you are most likely looking at a issue with the hardware, and in that case you should contact your local CCC in regards to a possible replacement under the warranty.

 

Best regards

Tonny

 

Tags (1)
Spardha
Crewman
Crewman
0 Likes
3
628

Re: AP4423 Possible open fuse Source A

Doesnt seem to have worked. Although I haven't been able to power cycle due to not being on-site.

Attachments
Tags (1)
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
2
626

Re: AP4423 Possible open fuse Source A

Hi

 

I think you might be looking at the wrong firmware there.

The firmware you are upgrading is the firmware for the Network management module in the unit.

 

If you navigate to [About] -> [Network] on the web interface, you can find the information under application module.

The version number presented there is the one you should be looking at.

 

Best regards

Tonny

Tags (1)
Spardha
Crewman
Crewman
0 Likes
1
624

Re: AP4423 Possible open fuse Source A

I see, its now v7.0.4 but the error is still present.

Tags (1)
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
622

Re: AP4423 Possible open fuse Source A

Hi 

 

In that case you are likely looking at a hardware issue.

I would suggest opening a case with your local CCC and get them involved, especially if the unit is under warranty.

 

Best regards

Tonny