Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. I apologize for the inconvenience this fault has caused you, let's go ahead and do some troubleshooting on the UPS.
The battery soft start fault occurs when the UPS fails to initiate its battery sub-system. This fault can be cleared by removing the load and doing the brain dead and cold start procedures on the UPS.
The Cold start procedure is used to determine if a UPS is functional or if it will not turn on when plugged into utility power. The Brain Dead procedure performs a hard reset of the Smart-Ups microprocessor. It does not however reset saved preferences.