3rd party PDU repairers

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 3rd party PDU repairers
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 04:38 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

0 Likes
7
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:38 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

3rd party PDU repairers

We have an AP7952 PDU that has just failed, but it is outside of warranty. APC doesn't repair these outside of warranty.

Can anyone tell me of a 3rd party repairer for these in Australia, preferably Sydney or at least NSW.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

right, so it just seemed strange to me since the LEDs on the management card are normal.

but anyway, maybe someone else knows of a repair place in your area ๐Ÿ˜•

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

most of us on the board are based in north america. did APC support in your region specifically state that nobody repairs these?

i don't know of anyone in the USA that repairs these so i'd assume its the same for Australia just because the type of product but i am wondering if support in that region would know - not sure if you asked since I know APC doesnt repair them (which you know.)

do you know whats wrong with it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:15 AM

hm ok so based on the fact the outlets are off, i would assume that yes, there is a problem with it. when the PDU is power cycled, if the outlets were set to off via the management card somehow, they should come back on regardless of their state before the power cycle.

i assume you used the correct 940-0144 cable (RJ12->DB9) via terminal and tried multiple computers just to be sure (9600, 8, N, 1, No flow control). i only say because the LEDs seem fairly normal..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

AFAIK there is no APC support centre in our region, but I stated clearly my location so I would assume they have taken that into account.

If there are no repairers in the US then that doesn't bode well for us here.

I'm fairly certain the management module is broken. We disconnected the PDU from the mains circuit for about 15 minutes then reconnected it, and after the management module booted up none of the outlets switched on. The management module appears to be completely unresponsive, both to network and serial. The PDU had been powered continuously for about a year and a half prior to this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

so there are no LEDs on the LCD display or network port?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

The management display shows all the normal signs of booting: the readout is blank, then shows 88 then eventually returns to 0; the line status is red, then transitions to green; the network port LEDs operate as per usual.

However none of the outlets turn on at all, and the management interface is not reachable at all by network or serial at any point during or after boot.

Message was edited by: anchor_systems

Message was edited by: anchor_systems

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

Well, all the ports were on prior to the PDU being disconnected from power, but that is irrelevant as the default state of the relays is off until the management module turns them on.

The correct cable was used (we have about 100 of these PDUs so cables are not in short supply), and I did try our standard remote console machine as well as another machine I use occasionally for configuring switches.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 04:39 AM . Last Modified: โ€Ž2024-03-18 04:14 AM

right, so it just seemed strange to me since the LEDs on the management card are normal.

but anyway, maybe someone else knows of a repair place in your area ๐Ÿ˜•

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of